Set E Questions 41 to 50
- 41
Per NEC 210.70(A)(2)(b), garage lighting control is:
Explanation
NEC 210.70(A)(2)(b) requires wall-switch-controlled lighting at garage entrances.
- 42
Per NEC 210.12(A), branch-circuit AFCI must be:
Explanation
NEC 210.12(A) requires combination-type AFCI at the branch-circuit origin for protection.
- 43
Per NEC Table 220.42, dwelling lighting demand allows:
Explanation
NEC Table 220.42 allows dwelling lighting at 100% to 3000 VA, then 35% for remainder.
- 44
Per NEC 210.8(D), which dwelling appliance needs GFCI?
Explanation
NEC 210.8(D) requires GFCI protection for branch circuits supplying dishwashers.
- 45
Per NEC 210.52(I), foyer receptacles required when area is:
Explanation
NEC 210.52(I) requires receptacle in foyers 60 ft² (5.6 m²) or greater.
- 46
Per NEC 210.8(A)(2), garage GFCI applies to receptacles at:
Explanation
NEC 210.8(A)(2) requires GFCI for 125V receptacles in garages and grade-level areas.
- 47
Per NEC 210.63, HVAC equipment receptacle requirement applies to:
Explanation
NEC 210.63 requires a receptacle within 25 ft (7.5 m) of HVAC in all occupancies.
- 48
Per NEC 210.52(A)(2)(3), fixed room dividers are treated as:
Explanation
NEC 210.52(A)(2)(3) treats fastened room dividers as wall space for receptacle placement.
- 49
Per NEC 210.8(A)(3), outdoor dwelling receptacles require:
Explanation
NEC 210.8(A)(3) requires GFCI for 125V receptacles installed outdoors at dwellings.
- 50
Per NEC 220.54, an electric dryer minimum load is:
Explanation
NEC 220.54 requires electric dryer minimum load of 5000 watts or nameplate, whichever is larger.