Topic 11 · Communications Systems
Set A Questions 1 to 10
- 1
What is the title of Article 800 in the NEC?
Explanation
NEC Article 800 covers communications circuits including telephone, telegraph, fire alarm, and similar systems.
- 2
What minimum voltage rating is required for communication cables?
Explanation
NEC 805.179: Communications wires and cables must have a voltage rating of not less than 300 volts.
- 3
Aerial communications circuits subject to accidental contact with power conductors over 300V must be protected with:
Explanation
NEC 805.90(A): A listed primary protector is required for circuits in aerial wire that may contact power conductors operating at over 300 volts to ground.
- 4
Where must a primary protector be located?
Explanation
NEC 805.90(B): The primary protector location shall be as close as practicable to the point of cable entrance into the building.
- 5
What is the minimum size of the grounding conductor for a primary protector?
Explanation
NEC 805.100(A)(3): The grounding conductor shall not be smaller than 14 AWG copper or other corrosion-resistant material.
- 6
In a one- or two-family dwelling, the primary protector grounding conductor must not exceed what length without a separate grounding electrode?
Explanation
NEC 805.100(A)(4): In one- and two-family dwellings, the grounding conductor shall not exceed 20 feet in length.
- 7
What is the minimum separation required between communications cables and power conductors when run parallel?
Explanation
NEC 805.133(A)(2): Communications wires and cables must be separated at least 2 inches from power conductors and Class 1 circuits.
- 8
What cable type is required for plenum installations?
Explanation
NEC 805.154(A): Type CMP (plenum-rated) cable must be used in ducts, plenums, and environmental air spaces.
- 9
For communications cables installed in vertical shafts penetrating multiple floors, the minimum required type is:
Explanation
NEC 805.154(B): Type CMR is required for riser applications. Type CMP (higher-rated) is also acceptable.
- 10
Where is Type CMX cable permitted?
Explanation
NEC 805.154(E): Type CMX is limited to dwellings or nonconcealed spaces with exposed runs not exceeding 10 feet.