Topic 11 · Communications Systems
Set B Questions 11 to 20
- 11
An unlisted communications cable may enter a building and run inside a maximum distance of:
Explanation
NEC 805.48: Unlisted outside plant cables are permitted inside a building if the inner run does not exceed 50 feet to the primary protector.
- 12
In a handhole enclosure, what separates communications cables from power cables?
Explanation
NEC 805.47: In handholes with both types, cables must be separated by a brick partition or by secure placement on opposing sides of the enclosure.
- 13
Which cable type is required for CATV systems in plenums?
Explanation
NEC 820.154(A): Type CATVP (plenum-rated) cable must be used in ducts, plenums, and environmental air spaces.
- 14
What is the minimum size of the grounding conductor for a CATV coaxial cable?
Explanation
NEC 820.100(A)(3): The grounding conductor for CATV coax shall not be smaller than 14 AWG.
- 15
What is the minimum separation between a rooftop CATV coaxial cable and power conductors over 300V?
Explanation
NEC 820.44(E)(1): Coaxial cables on buildings must maintain 8 feet separation from open power conductors operating above 300 volts.
- 16
Network-Powered Broadband Systems provide voice, video, data, and what else?
Explanation
NEC Article 830: These systems provide services AND power for networking equipment within the building.
- 17
What is the maximum voltage for a medium-power broadband system?
Explanation
NEC Table 830.15: Medium-power systems operate at voltages up to 150 volts.
- 18
Class 2 and Class 3 circuits are covered in which article and chapter?
Explanation
NEC Article 725 (in Chapter 7) covers Class 2 and Class 3 circuits. Since the 2023 NEC, Class 1 circuits have their own Article 724, and the general wiring rules for Class 2 and 3 cables are in Article 722.
- 19
When Chapter 8 rules conflict with Chapters 1-4, which rules apply?
Explanation
NEC 90.3: Chapter 8 is independent except where Chapters 1-7 are specifically referenced.
- 20
Communications cables exposed on ceilings must be supported by fittings designed to:
Explanation
NEC 805.24: Mechanical support must be done so as not to damage the cable during normal building use.