Topic 11 · Communications Systems
Set C Questions 21 to 30
- 21
Can communications cables be strapped to the exterior of a conduit?
Explanation
NEC 805.133(B): Communications cables shall not be strapped to the exterior of any conduit or raceway.
- 22
What must be done with accessible abandoned communications cables?
Explanation
NEC 805.25: The accessible portion of abandoned communications cables shall be removed.
- 23
What type of optical fiber cable is required in environmental air plenums?
Explanation
NEC 770.154(A): Type OFNP (optical fiber nonconductive plenum) must be used in plenums and environmental air spaces.
- 24
Where does a Premises-Powered Broadband System obtain its power?
Explanation
NEC Article 840: This system is powered from the subscriber's own premises, unlike network-powered systems.
- 25
Can optical fiber cables and copper communications cables share a raceway?
Explanation
NEC 770.133(A): Nonconductive optical fiber cables may be placed in the same raceway with communications cables.
- 26
A communications grounding electrode must be bonded to the power system electrode using:
Explanation
NEC 805.100(D): A bonding jumper not smaller than 6 AWG copper connects the communications electrode to the power grounding system.
- 27
For a building with no existing ground, the communications electrode must be:
Explanation
NEC 805.100(B)(2): If no power system ground exists, use a ground rod not less than 5 feet long and 1/2 inch in diameter.
- 28
What device connects communications system grounding conductors to the power system ground?
Explanation
NEC 250.94: An Intersystem Bonding Termination (IBT) provides an accessible connection point for communications bonding conductors.
- 29
The intersystem bonding termination must accommodate at least how many bonding conductors?
Explanation
NEC 250.94(A): An IBT shall have capacity for connection of not less than three intersystem bonding conductors.
- 30
When communications cables penetrate fire-rated walls, what action is required?
Explanation
NEC 805.26: Penetrations through fire-rated assemblies must be firestopped using approved methods to maintain the fire-resistance rating.