Topic 11 · Communications Systems
Set D Questions 31 to 40
- 31
Type CMUC undercarpet cable is permitted in which applications?
Explanation
NEC 805.154: Type CMUC is specifically listed for installation under carpet in any occupancy type.
- 32
On a shared utility pole, communications wires should be positioned:
Explanation
NEC 805.44(A)(3) and NESC practice: Communications cables run below power conductors on joint-use poles.
- 33
The minimum separation between communications wires and power conductors on a pole is:
Explanation
NEC 805.44(A)(4): Communications wires must maintain at least 39 inches separation from power conductors where practicable.
- 34
Audio signal wiring for paging systems is covered by:
Explanation
NEC Article 640 covers Audio Signal Processing, Amplification, and associated wiring systems.
- 35
Antenna systems for television and radio receivers are covered by which article?
Explanation
NEC Article 810 covers antenna systems for radio and television receiving equipment.
- 36
What is the minimum copper conductor size for radio/TV receiving antenna grounding?
Explanation
NEC 810.21(H): The grounding conductor shall not be smaller than 10 AWG copper.
- 37
Where must an antenna discharge unit (lightning arrestor) be located?
Explanation
NEC 810.20(B): The antenna discharge unit must be located outside or inside between the entrance point and the receiver.
- 38
Must an antenna grounding electrode be bonded to the power system ground?
Explanation
NEC 810.21(J): A bonding jumper (not smaller than 6 AWG) must connect antenna grounding to the power electrode system.
- 39
What provides safety from shock and fire in Class 2 circuits?
Explanation
NEC 725.121: A Class 2 power source is listed to limit voltage and current output to safe levels.
- 40
Can you run Class 2 thermostat wire in the same conduit as 120V power?
Explanation
NEC 725.136(A): Class 2 conductors cannot be in the same cable, conduit, or raceway with power conductors.