Topic 11 · Communications Systems
Set E Questions 41 to 50
- 41
Fire alarm systems are categorized as either Power-Limited or:
Explanation
NEC Article 760 covers both Non-Power-Limited Fire Alarm (NPLFA) and Power-Limited Fire Alarm (PLFA) circuits.
- 42
Fire alarm circuit outlet boxes are typically identified by which color?
Explanation
NEC 760.30 and standard practice: Fire alarm pathways are identified with red boxes to prevent unintentional interference.
- 43
Power-Limited Fire Alarm cable in a vertical riser must be type:
Explanation
NEC 760.154(B): Vertical runs must use Type FPLR as minimum, or Type FPLP which is acceptable.
- 44
Can communications cable (CMP, CMR) substitute for PLFA cable?
Explanation
NEC 760.154: Type CMP can substitute for FPLP; Type CMR for FPLR due to equivalent fire ratings.
- 45
Class 1 circuit conductors must have insulation rated for:
Explanation
NEC 725.49(B): Class 1 insulated conductors shall be suitable for 600 volts.
- 46
A Class 1 power-limited source must be rated not more than:
Explanation
NEC 725.41(A): Class 1 power-limited circuits are supplied from a source with rated output not exceeding 30 volts and 1000 volt-amperes.
- 47
When running large bundles of Power over Ethernet (PoE) cables, what must be addressed?
Explanation
NEC 725.144: Large bundles carrying PoE generate significant heat that can damage insulation per ampacity tables.
- 48
Special PoE cables with higher ampacity limits use the cable suffix:
Explanation
NEC 725.144(E): Limited Power (LP) suffix cables are designed and tested for higher current carrying in tight bundles.
- 49
Optical fiber cables with no metallic armor or conductors are called:
Explanation
NEC 770.2: Nonconductive optical fiber cables contain no electrically conductive materials or armor.
- 50
What is the minimum size bonding jumper for an Intersystem Bonding Termination?
Explanation
NEC 250.94(A)(4): The bonding jumper connecting the IBT to the grounding electrode system shall not be smaller than 6 AWG copper or 4 AWG aluminum.