Topic 01 · General Requirements
Set A Questions 1 to 10
- 1
What is the primary purpose of NEC Article 90.1(A)?
Explanation
NEC 90.1(A): "The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity."
- 2
Per NEC Article 100, what does "Accessible" mean for equipment?
Explanation
NEC Article 100: Accessible equipment "admits close approach; not guarded by locked doors, elevation, or other effective means."
- 3
What NEC term is maximum current a conductor can carry?
Explanation
NEC Article 100 defines ampacity as "the maximum current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating."
- 4
NEC 90.2(A) covers which type of installation?
Explanation
NEC 90.2(A) covers "installations of conductors and equipment within or on public and private buildings, structures, mobile homes, recreational vehicles, and floating buildings."
- 5
How does NEC define the difference between feeders and branch circuits?
Explanation
NEC Article 100: A feeder connects the service equipment to the final branch-circuit overcurrent device, while a branch circuit connects the final overcurrent device to outlets.
- 6
Per NEC Article 100, what is a branch circuit?
Explanation
NEC Article 100 defines a branch circuit as "the circuit conductors between the final overcurrent device protecting the circuit and the outlet(s)."
- 7
NEC Article 100 defines a dwelling unit as:
Explanation
NEC Article 100: A dwelling unit is "a single unit providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation."
- 8
NEC Article 100 defines continuous load as:
Explanation
NEC Article 100: A continuous load is "a load where the maximum current is expected to continue for 3 hours or more."
- 9
Per NEC 110.14(A), conductor terminals must use:
Explanation
NEC 110.14(A) states "connection of conductors shall ensure a thoroughly good connection without damaging the conductors," requiring proper preparation and stripping.
- 10
NEC 110.14(B) requires terminals to consider:
Explanation
NEC 110.14(B) states "the temperature rating for terminations shall be considered, conductors used at temperatures not exceeding the lowest rated component."