- 11
Per NEC 110.26(A)(1), minimum clear working space depth is:
Explanation
NEC 110.26(A)(1), Condition 1 (0–150V to ground) requires "a minimum of 3 ft (914 mm) clear working space in front of electrical equipment."
- 12
NEC 110.26(A)(3) requires minimum headroom of:
Explanation
NEC 110.26(A)(3) requires "a minimum headroom of 6½ ft (1981 mm) for working spaces about service equipment, switchboards, switchgear, panelboards, or motor control centers."
- 13
NEC 110.26(A)(2) requires working space width of:
Explanation
NEC 110.26(A)(2) requires "clear working space width not less than 30 in. (762 mm) or the width of the equipment, whichever is greater."
- 14
Per NEC 110.12, electrical equipment must be:
Explanation
NEC 110.12 states "electrical equipment shall be installed in a neat and workmanlike manner."
- 15
Per NEC Article 100, "listed" means:
Explanation
NEC Article 100: "Listed" means "equipment, materials, or services included in a list published by an organization that is acceptable to the AHJ."
- 16
How does NEC Article 100 distinguish "labeled" from "listed"?
Explanation
NEC Article 100: "Labeled" means "bearing a label... from an acceptable listing organization." Listed means it appears on that organization's published list.
- 17
Per NEC Article 100, "approved" means:
Explanation
NEC Article 100 defines "approved" as "acceptable to the authority having jurisdiction."
- 18
NEC 90.4 gives enforcement authority to:
Explanation
NEC 90.4 states "the authority having jurisdiction is responsible for making interpretations and approving equipment, materials, and installations."
- 19
NEC 90.5(A) identifies mandatory rules with:
Explanation
NEC 90.5(A) identifies mandatory rules by use of "shall" or "shall not." Permissive rules use "shall be permitted."
- 20
NEC 90.3 describes relationship of Chapters 1–4 to 5–7:
Explanation
NEC 90.3 states "Chapters 1, 2, 3, and 4 apply generally. Chapters 5, 6, and 7 can supplement or modify the general rules."