Topic 01 · General Requirements
Set C Questions 21 to 30
- 21
NEC Chapter 9 applies:
Explanation
NEC 90.3 states "Chapter 9 consists of tables that are applicable as referenced in the Code."
- 22
Per NEC 110.3(B), listed equipment must be:
Explanation
NEC 110.3(B) requires "listed or labeled equipment to be installed and used in accordance with any instructions included in the listing or labeling."
- 23
NEC Article 100 defines a device as:
Explanation
NEC Article 100: A device is "a unit of an electrical system... that carries or controls electric energy as its principal function."
- 24
NEC Article 100 defines "dusttight" as:
Explanation
NEC Article 100: "Dusttight" is "constructed so that dust will not enter the enclosing case under specified test conditions."
- 25
Per NEC Article 100, a raceway is:
Explanation
NEC Article 100 defines raceway as "an enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or busbars."
- 26
NEC 110.26(C)(1) requires exits at each end for:
Explanation
NEC 110.26(C)(1) requires "at least one entrance at each end of the working space for equipment rated 1200A or more and over 6 ft (1.8 m) wide."
- 27
Per NEC 110.27(A), live parts at 50V+ must be:
Explanation
NEC 110.27(A) requires "live parts of electrical equipment operating at 50 volts or more to be guarded against accidental contact by approved enclosures or other approved means."
- 28
NEC 110.14(C) requires terminations at 100A or less use:
Explanation
NEC 110.14(C)(1)(a) requires "terminations for circuits rated 100A or less use the 60°C ampacity column unless the equipment is listed for higher temperatures."
- 29
For circuits over 100A, NEC 110.14(C) permits:
Explanation
NEC 110.14(C)(1)(b) states "conductors rated for circuits over 100A shall use the 75°C ampacity column, unless the equipment is listed for higher temperatures."
- 30
NEC Article 100 defines separately derived system as:
Explanation
NEC Article 100: A separately derived system is "a premises wiring system whose power is derived from a source other than a service, with no direct connection to supply conductors of another system."