Topic 01 · General Requirements
Set D Questions 31 to 40
- 31
NEC Article 100 defines qualified person as:
Explanation
NEC Article 100: A qualified person is "one who has skills and knowledge related to the construction and operation of the electrical equipment and installations and has received safety training."
- 32
NEC 110.9 requires equipment to have interrupting rating:
Explanation
NEC 110.9 requires equipment intended to interrupt current at fault levels to have an interrupting rating not less than the nominal circuit voltage and the current available at the equipment terminals.
- 33
NEC 110.10 requires overcurrent devices to:
Explanation
NEC 110.10 requires overcurrent protective devices, total impedance, equipment short-circuit ratings, and characteristics to be selected and coordinated to permit the circuit protective devices to clear a fault without extensive damage.
- 34
What does NEC Article 100 define as a "receptacle"?
Explanation
Article 100 defines a receptacle as a contact device installed at the outlet for the connection of an attachment plug, or for the direct connection of electrical utilization equipment.
- 35
Per NEC Article 100, what is an "outlet"?
Explanation
Article 100 defines an outlet as a point on the wiring system at which current is taken to supply utilization equipment.
- 36
NEC Article 100 defines "overcurrent" as any current that exceeds:
Explanation
Article 100 defines overcurrent as any current in excess of the rated current of equipment or the ampacity of a conductor, whether caused by overload, short circuit, or ground fault.
- 37
What minimum illumination does NEC 110.26(D) require at working spaces about service equipment?
Explanation
NEC 110.26(D) requires that illumination shall be provided for all working spaces about service equipment, switchboards, switchgear, panelboards, or motor control centers. The NEC requires adequate illumination without specifying a foot-candle value.
- 38
Per NEC 110.26(E)(1), what is required in large equipment rooms with equipment rated 1200A or more?
Explanation
NEC 110.26(E)(1)(a) requires at least one 125V, single-phase, 15- or 20-ampere receptacle outlet in service equipment rooms for equipment rated 1200A or more. Additionally, 110.26(D) requires adequate illumination.
- 39
According to NEC 110.22(A), what must be placed on each disconnecting means?
Explanation
NEC 110.22(A) requires each disconnecting means to be legibly marked to indicate its purpose unless located and arranged so the purpose is evident.
- 40
Per NEC 90.2(B)(5), which type of installation is NOT covered by the Code?
Explanation
NEC 90.2(B)(5) excludes installations under the exclusive control of an electric utility that are used for generation, transmission, distribution, or communication, and are on property owned or leased by the utility.