Topic 01 · General Requirements
Set E Questions 41 to 50
- 41
What does NEC Article 100 define as a "bonding jumper"?
Explanation
Article 100 defines a bonding jumper as a reliable conductor to ensure the required electrical conductivity between metal parts required to be electrically connected.
- 42
Per NEC Article 100, what is a "panelboard"?
Explanation
Article 100 defines a panelboard as a single panel or group of panel units with buses and automatic overcurrent devices, placed in a cabinet or cutout box accessible from the front only.
- 43
Per NEC 110.11, what must electrical equipment be suitable to withstand when installed?
Explanation
NEC 110.11 requires that equipment be suitable for the environment where it is installed, considering exposure to corrosive agents, dampness, chemicals, and other conditions.
- 44
NEC 110.21(B) requires field-applied hazard markings to be what?
Explanation
NEC 110.21(B) requires field-applied labels or markings to be of sufficient durability to withstand the environment involved. The marking must be effective for its purpose.
- 45
NEC Article 100 defines "ground fault" as:
Explanation
Article 100 defines a ground fault as an unintentional, electrically conducting connection between an ungrounded conductor of an electrical circuit and the normally non–current-carrying conductors, metallic enclosures, metallic raceways, metallic equipment, or earth.
- 46
Which NEC section covers requirements for electrical connections and splices?
Explanation
NEC 110.14 covers the requirements for electrical connections including terminals, splices, and temperature limitations.
- 47
Per NEC 90.1(C), the Code is NOT intended to be used as:
Explanation
NEC 90.1(C) states the Code is not intended as a design specification or instruction manual for untrained persons.
- 48
According to NEC Article 100, what is a "service"?
Explanation
Article 100 defines a service as the conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.
- 49
Per NEC 110.26(A)(1), what is the minimum working clearance for Condition 2 at 151V–600V to ground?
Explanation
NEC Table 110.26(A)(1), Condition 2 (exposed live parts on one side and grounded parts on the other) at 151–600V requires a minimum of 3½ ft (1067 mm) clear working space.
- 50
According to NEC Article 100, what is the definition of "equipment"?
Explanation
Article 100 defines equipment as a general term, including fittings, devices, appliances, luminaires, apparatus, machinery, and the like, used as part of or in connection with an electrical installation.