Topic 05 · Grounding & Bonding
Set A Questions 1 to 10
- 1
What is the primary purpose of grounding an electrical system?
Explanation
NEC 250.4(A)(1): Electrical systems that are grounded shall be connected to earth to limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines.
- 2
Bonding metallic parts of an electrical system accomplishes what?
Explanation
NEC 250.4(A)(3): Normally non-current-carrying conductive materials likely to become energized shall be connected to establish an effective ground-fault current path.
- 3
An effective ground-fault path must have which characteristics?
Explanation
NEC 250.4(A)(5): An effective ground-fault current path must have low impedance to facilitate overcurrent device operation.
- 4
Is the earth considered an effective ground-fault current path?
Explanation
NEC 250.4(A)(5): The earth shall not be considered as an effective ground-fault current path.
- 5
What defines a grounding electrode?
Explanation
NEC Article 100: Grounding Electrode is a conducting object through which a direct connection to earth is established.
- 6
Which is NOT permitted as a grounding electrode?
Explanation
NEC 250.52(B)(1): Metal underground gas piping systems shall not be used as a grounding electrode.
- 7
A metal water pipe grounding electrode must be in earth contact for at least:
Explanation
NEC 250.52(A)(1): A metal underground water pipe must have 3.0 m (10 ft) or more in direct contact with the earth.
- 8
A concrete-encased (Ufer) electrode requires what minimum length?
Explanation
NEC 250.52(A)(3): A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of bare copper conductor or steel reinforcing bars.
- 9
What is the required minimum length for a rod electrode?
Explanation
NEC 250.52(A)(5): Rod and pipe electrodes shall not be less than 2.44 m (8 ft) in length.
- 10
A single electrode is supplemented if its earth resistance exceeds:
Explanation
NEC 250.53(A)(2): If a single rod, pipe, or plate electrode has resistance to earth of 25 ohms or less, supplemental electrode is not required.