Supplemental rod electrodes must be spaced at least:
Explanation
NEC 250.53(A)(3): If multiple rod, pipe, or plate electrodes are installed, they shall not be less than 1.8 m (6 ft) apart.
- 12
A ground ring electrode must be buried at depth of minimum:
Explanation
NEC 250.53(F): The ground ring shall be buried at depth below surface of not less than 750 mm (30 in.).
- 13
Which conductor connects the system to a grounding electrode?
Explanation
NEC Article 100: Grounding Electrode Conductor connects the system grounded conductor or equipment to a grounding electrode or point on the grounding electrode system.
- 14
Grounding electrode conductor size is primarily determined by:
Explanation
NEC 250.66: Grounding electrode conductor sizes are based on the size of the largest ungrounded service-entrance conductor or equivalent area for parallel conductors.
- 15
A sole connection to a single rod electrode is not larger than:
Explanation
NEC 250.66(A): Where connected to rod, pipe, or plate electrodes, the sole connection portion shall not be larger than 6 AWG copper wire.
- 16
A sole connection to a concrete-encased electrode is not larger than:
Explanation
NEC 250.66(B): The sole connection to a concrete-encased electrode shall not be larger than 4 AWG copper wire.
- 17
The main bonding jumper connects what two components?
Explanation
NEC Article 100 & 250.28: Main Bonding Jumper connects the grounded circuit conductor to the equipment grounding conductor at the service.
- 18
Main bonding jumper size is based on:
Explanation
NEC 250.28(D)(1): Main bonding jumpers shall be sized per Table 250.102(C)(1), based on the largest ungrounded service conductor.
- 19
Equipment grounding conductor size depends on:
Explanation
NEC 250.122(A): Equipment grounding conductors shall not be smaller than shown in Table 250.122, based on the overcurrent device rating.
- 20
When ungrounded wires increase in size, the EGC must:
Explanation
NEC 250.122(B): Equipment grounding conductors shall be increased in size proportionately to the circular mil area of the ungrounded conductors.