Topic 05 · Grounding & Bonding
Set C Questions 21 to 30
- 21
The neutral can ground equipment where located:
Explanation
NEC 250.142(A): The grounded conductor is permitted to ground non-current-carrying metal parts on the supply side or within the service-disconnecting means enclosure.
- 22
On the load side of service, grounding with neutral is:
Explanation
NEC 250.142(B): Except specific exceptions, the grounded conductor shall not ground non-current-carrying metal parts on the load side of service disconnect.
- 23
Interior metal water piping is bonded using:
Explanation
NEC 250.104(A)(1): Metal water piping system bonding jumper shall be sized in accordance with Table 250.102(C)(1).
- 24
Other metal piping bonding uses:
Explanation
NEC 250.104(B): Other metal piping bonding sized per Table 250.122 using the equipment grounding conductor of the circuit likely to energize it.
- 25
An isolated ground receptacle is identified by:
Explanation
NEC 250.146(D): Isolated ground receptacles shall be identified by an orange triangle located on the face of the receptacle.
- 26
Service raceways must be connected to:
Explanation
NEC 250.80: Metal enclosures for service conductors shall be connected to the grounded system conductor if the system is grounded.
- 27
Locknuts alone are not sufficient for service bonding. Use:
Explanation
NEC 250.92(B): Standard locknuts or bushings must be supplemented by threaded hubs, bonding jumpers, or other listed bonding devices.
- 28
Load-side equipment bonding jumper size uses:
Explanation
NEC 250.102(D): Equipment bonding jumper on load side of service shall be sized per Table 250.122 based on overcurrent device rating.
- 29
A separately derived system bonding jumper connects at:
Explanation
NEC 250.30(A)(1): System bonding jumper shall be connected at any single point on the separately derived system from source to first disconnect.
- 30
A feeder to a separate building must include EGC and:
Explanation
NEC 250.32(B)(1): To prevent parallel neutral paths, the neutral shall not be connected to the equipment grounding conductor at the separate building.