Topic 05 · Grounding & Bonding
Set D Questions 31 to 40
- 31
Aluminum GEC outside must not terminate within:
Explanation
NEC 250.64(A): Aluminum grounding electrode conductors shall not be terminated within 450 mm (18 in.) of the earth when used outdoors.
- 32
LFMC can serve as EGC if protected by OCPD of:
Explanation
NEC 250.118(6): LFMC is permitted for trade size 3/8-1/2 protected by 20A or less, or 3/4-1-1/4 by 60A or less, length not exceeding 6 feet.
- 33
Wire-type equipment grounding conductors can be:
Explanation
NEC 250.119: Equipment grounding conductors shall be permitted to be bare, covered, or insulated.
- 34
Hospital patient care areas require:
Explanation
NEC 517.13(A) and (B): Patient care space branch circuits requiring effective ground-fault path by metal raceway system AND insulated copper EGC.
- 35
Fixed equipment located within 8 feet vertically must ground if near:
Explanation
NEC 250.110(1): Equipment in wet/damp locations or within 8 ft vertically or 5 ft horizontally of ground or grounded metal objects must be grounded.
- 36
Multiple circuits in one conduit require EGC sized for:
Explanation
NEC 250.122(C): Single equipment grounding conductor with multiple circuits shall be sized for the largest overcurrent device protecting any conductor.
- 37
Equipment grounding conductor splicing uses:
Explanation
NEC 250.148: Equipment grounding conductor continuity in boxes may be established by listed devices, wire nuts, compression connectors, or exothermic welding.
- 38
System Bonding Jumper connects what at derived systems?
Explanation
NEC Article 100: System Bonding Jumper is the connection between grounded conductor and supply-side bonding jumper or EGC at separately derived system.
- 39
Water meter insulation requires bonding:
Explanation
NEC 250.68(B): Bonding jumpers must be installed around insulated joints and equipment like water meters that may be disconnected during repairs.
- 40
Building structural frame usable as electrode if:
Explanation
NEC 250.52(A)(2): Metal frame of building is grounding electrode if at least one member is in direct earth contact for 10 ft or encased in concrete.