Topic 05 · Grounding & Bonding
Set E Questions 41 to 50
- 41
High-impedance grounded neutral systems operate at:
Explanation
NEC 250.36: High-impedance grounded neutral systems are permitted for 3-phase systems of 480 to 1000 volts with ground-fault current limiting impedance.
- 42
An 8 AWG GEC must be protected by:
Explanation
NEC 250.64(B)(3): An 8 AWG grounding electrode conductor must be protected by rigid metal conduit, IMC, PVC, EMT, or cable armor.
- 43
A screw main bonding jumper must have:
Explanation
NEC 250.28(B): Where main bonding jumper is a screw only, it shall be identified with green finish visible with screw installed.
- 44
Supply-side bonding jumper is installed on the:
Explanation
NEC Article 100: Supply-side bonding jumper is a conductor installed on the supply side of service or within service equipment enclosure.
- 45
For 500 kcmil copper entrance conductors, supply-side bonding jumper is:
Explanation
NEC Table 250.102(C)(1): For 500 kcmil copper ungrounded conductors, supply-side bonding jumper shall be 1/0 AWG copper.
- 46
Knockouts at service require bonding using:
Explanation
NEC 250.92(B): Bonding jumpers must be used around concentric or eccentric knockouts that impair electrical connection to ground.
- 47
Communications GEC length limit in one/two-family homes:
Explanation
NEC 800.100(A)(4): Grounding electrode conductor for communications shall be as short as practicable, not exceeding 6.0 m (20 ft).
- 48
Bonding in hazardous locations requires:
Explanation
NEC 250.100: Locknut/bushing alone are insufficient in hazardous locations; bonding jumpers with proper fittings or approved means must be used.
- 49
Equipment in wet/damp locations not isolated must be:
Explanation
NEC 250.110(3): Fixed equipment in wet or damp locations not isolated shall be connected to an equipment grounding conductor.
- 50
Isolated ground receptacle conductor must terminate:
Explanation
NEC 250.146(D): The isolated ground conductor shall pass through panelboards without connecting to grounding terminals, terminating directly back at the service or derived system grounding terminal.