Topic 09 · Hazardous Locations
Set A Questions 1 to 10
- 1
Which location classification describes areas where ignitable concentrations of flammable gases can exist under normal operating conditions?
Explanation
NEC 500.5(B)(1): Class I, Division 1 location is a location in which ignitable concentrations of flammable gases, flammable liquid-produced vapors, or combustible liquid-produced vapors can exist under normal operating conditions.
- 2
Class II hazardous locations are distinguished by the presence of what material?
Explanation
NEC 500.5(C): Class II Locations are those that are hazardous because of the presence of combustible dust.
- 3
Locations with easily ignitable fibers or combustible flyings not normally suspended in air are classified as:
Explanation
NEC 500.5(D): Class III Locations are hazardous because of easily ignitable fibers or materials producing combustible flyings, but fibers/flyings are not likely to be in suspension in quantities sufficient to produce ignitable mixtures.
- 4
Flammable liquids in closed containers or systems from which they escape only by accidental rupture are classified as:
Explanation
NEC 500.5(B)(2): Class I, Division 2 location is one where volatile flammable liquids are normally confined within closed containers or systems from which they can escape only in case of accidental rupture or breakdown.
- 5
Which wiring method is not permitted in Class I, Division 1 locations?
Explanation
NEC 501.10(A)(1): Wiring methods in Class I, Division 1 are restricted to threaded RMC, threaded steel IMC, or Type MI cable. EMT is not permitted because it lacks threads and cannot contain explosions.
- 6
What is the primary function of an explosionproof enclosure in Class I locations?
Explanation
NEC Article 100: Explosionproof Equipment is enclosed in a case capable of withstanding explosion of gas/vapor within it and preventing ignition of surrounding atmosphere by sparks or flashes escaping through machined joints.
- 7
Conduit seals in Class I, Division 1 must be placed within ____ of the enclosure when apparatus may produce arcs or sparks.
Explanation
NEC 501.15(A)(1): Conduit seals shall be installed within 450 mm (18 in.) of the enclosure.
- 8
A sealing fitting at a Class I location boundary must be positioned within what distance of the boundary?
Explanation
NEC 501.15(A)(4) and (B)(2): The sealing fitting shall be located within 3.0 m (10 ft) on either side of the location boundary, with no unions, couplings, or boxes between the seal and where the conduit leaves the hazardous area.
- 9
Minimum sealing compound thickness in a conduit seal is:
Explanation
NEC 501.15(C)(3): Sealing compound thickness shall not be less than the metric designator of the fitting, and in no case less than 16 mm (5/8 in.).
- 10
Are splices and taps permitted inside sealing fittings?
Explanation
NEC 501.15(C)(4): Splices and taps shall not be made in fittings intended only for sealing with compound.