Topic 09 · Hazardous Locations
Set B Questions 11 to 20
- 11
Which Class I Group includes atmospheres containing acetylene?
Explanation
NEC 500.6(A)(1): Group A atmospheres contain acetylene.
- 12
Hydrogen and combustible gases with over 30% hydrogen content belong to:
Explanation
NEC 500.6(A)(2): Group B atmospheres contain hydrogen and combustible process gases with more than 30 percent hydrogen by volume.
- 13
Gasoline, propane, and natural gas are classified as:
Explanation
NEC 500.6(A)(4): Group D atmospheres contain flammable gases such as gasoline, propane, methane, and butane.
- 14
Which Class II Group includes metallic dusts like aluminum and magnesium?
Explanation
NEC 500.6(B)(1): Group E atmospheres contain combustible metal dusts including aluminum, magnesium, and their commercial alloys.
- 15
Coal, carbon black, and charcoal dust belong to Class II:
Explanation
NEC 500.6(B)(2): Group F atmospheres contain combustible carbonaceous dusts with more than 8 percent total entrapped volatiles, such as coal, carbon black, and charcoal.
- 16
Grain elevators, flour mills, and agricultural dusts fall under Class II:
Explanation
NEC 500.6(B)(3): Group G atmospheres contain combustible dusts not included in Groups E or F, including flour, grain, wood, and plastic.
- 17
Cotton lint and sawdust are associated with which hazardous location class?
Explanation
NEC 500.5(D): Class III Locations are hazardous because of easily ignitable fibers such as cotton, wool, and materials producing combustible flyings.
- 18
In a commercial garage, the area within ____ of the floor is typically Class I, Division 2.
Explanation
NEC 511.3(C)(1)(a): The entire area up to 450 mm (18 in.) above the floor in major repair garages is classified as Class I, Division 2 unless adequate ventilation is provided.
- 19
Inside a fuel dispenser enclosure at gas stations, the classification is:
Explanation
NEC Table 514.3(B)(1): The space within the dispenser enclosure and all electrical equipment integral with the dispensing hose or nozzle is Class I, Division 1.
- 20
Outside a fuel dispenser, the Class I, Division 2 area extends horizontally ____ and vertically to ____ above grade.
Explanation
NEC Table 514.3(B)(1): Up to 450 mm (18 in.) above grade within 6.0 m (20 ft) horizontally from any edge of the dispenser enclosure is Class I, Division 2.