Topic 09 · Hazardous Locations
Set C Questions 21 to 30
- 21
Intrinsically safe apparatus can be installed in hazardous locations if properly:
Explanation
NEC 504.20: Intrinsically safe apparatus and wiring shall be permitted in any hazardous location for which it is identified and must be installed per the control drawing.
- 22
Intrinsically safe conductors must be separated from nonintrinsically safe conductors by at least:
Explanation
NEC 504.30(A)(2): Conductors of intrinsically safe circuits shall be separated at least 50 mm (2 in.) from conductors of nonintrinsically safe circuits.
- 23
How are intrinsically safe circuit conductors typically identified?
Explanation
NEC 504.80(C): Intrinsically safe conductors may be color-coded light blue where no other light blue conductors are used.
- 24
In an aircraft hangar, which area is Class I, Division 1?
Explanation
NEC 513.3(A): Any pit or depression below hangar floor level shall be classified as Class I, Division 1, extending up to floor level.
- 25
The aircraft hangar floor area up to ____ high is Class I, Division 2.
Explanation
NEC 513.3(C)(1): The entire hangar floor area up to 450 mm (18 in.) above the floor is classified as Class I, Division 2.
- 26
Electrical equipment inside spray paint booths must be approved for:
Explanation
NEC 516.3(A): The interior of spray booths is classified as Class I, Division 1 or Zone 1, and electrical wiring and equipment shall be approved for the location.
- 27
Standard fluorescent luminaires inside spray paint booths must be:
Explanation
NEC 516.4(C): Lighting inside spray booths must be listed for Class I, Division 1 atmospheres or separated by tight glass panels meeting specific requirements.
- 28
Operating rooms using flammable anesthetics are classified as:
Explanation
NEC 517.60: Any room or space where flammable anesthetics or volatile flammable disinfecting agents are stored is classified as Class I, Division 1.
- 29
Threaded RMC connections in Class I, Division 1 require at least ____ fully engaged threads.
Explanation
NEC 500.8(E)(1): Equipment with threatened entries for NPT threaded conduit shall be made up with at least five threads fully engaged.
- 30
Type X purged and pressurized Class I, Division 1 enclosures reduce classification inside to:
Explanation
NFPA 496 and NEC 500.7(D): Type X purging reduces the classification inside a properly purged and pressurized enclosure from Class I, Division 1 to unclassified.