Topic 09 · Hazardous Locations
Set D Questions 31 to 40
- 31
Which wiring method is allowed in Class II, Division 1 locations?
Explanation
NEC 502.10(A)(1): Wiring methods for Class II, Division 1 include threaded RMC, threaded IMC, Type MI cable, and listed Type MC cable with dusttight fittings.
- 32
Switches in Class II, Division 1 locations must be housed in ____ enclosures.
Explanation
NEC 502.115(A): Switches, circuit breakers, motor controllers, and fuses in Class II, Division 1 must be provided with dust-tight enclosures.
- 33
Conduit seals in Class II locations are required where:
Explanation
NEC 502.15: Seals required where a raceway provides communication between a dust-tight enclosure and one that is not, to prevent dust entry.
- 34
Which wiring method is permitted in Class III, Division 1 locations?
Explanation
NEC 503.10(A): Wiring methods for Class III, Division 1 include RMC, RNC, IMC, EMT, dust-tight wireways, or Type MI, MC, or SNM cable.
- 35
Equipment in Class III locations must prevent ignition of collected material by:
Explanation
NEC Article 503: Class III equipment must prevent ignition of collected fibers and flyings by heat, sparks, or arcs, with dust-tight enclosures to prevent fiber accumulation.
- 36
Class I, Zone 0 is similar to which Division designation?
Explanation
NEC 505.5(B)(1): Zone 0 is where ignitable concentrations of flammable gases are present continuously or for extended periods.
- 37
Which Zone designation equals Class I, Division 1?
Explanation
NEC 505.5(B)(2): Zone 1 is where ignitable concentrations are likely to exist under normal operating conditions.
- 38
Class I, Division 2 is most similar to which Zone classification?
Explanation
NEC 505.5(B)(3): Zone 2 is where ignitable concentrations are not likely in normal operation and will exist only for brief periods.
- 39
Equipment listed for Class I, Division 1 can be used in Class I, Zone 1 if:
Explanation
NEC 505.9(C)(1): Equipment listed and marked for Class I, Division 1 or Division 2 shall be permitted in Class I, Zone 1 or Zone 2 locations, respectively, for the same gas and with suitable temperature class.
- 40
Can Zone 1 listed equipment be installed in Class I, Division 1 locations?
Explanation
Zone 1 equipment is not evaluated for continuous gas presence (Zone 0 condition), so it cannot be used in Division 1 which encompasses both Zone 1 and Zone 0 scenarios.