Topic 09 · Hazardous Locations
Set E Questions 41 to 50
- 41
Inside a fixed-roof storage tank for flammable liquids, the classification is:
Explanation
NEC Table 515.3: Inside a fixed roof tank (bulk storage plant) is classified as Class I, Division 1.
- 42
Explosionproof motors prevent ignition of surrounding gas by:
Explanation
The explosionproof enclosure allows gas entry. If ignited, the heavy enclosure withstands pressure, and machined flanges cool escaping gases below the ignition temperature of the outside atmosphere.
- 43
Receptacles in Class I, Division 2 locations (repair garages) must be:
Explanation
NEC 511.4(B)(2): Receptacles in Class I, Division 2 areas shall be approved for Class I, Division 1 locations, unless positioned above the classified zone.
- 44
Flexible cords in Class II, Division 1 for dusttight equipment must be rated:
Explanation
NEC 502.140: Flexible cords shall be permitted for connections to dusttight equipment if listed for extra-hard usage, containing an equipment grounding conductor.
- 45
Portable lighting in Class I, Division 1 locations must be:
Explanation
NEC 501.130(A): Portable lighting equipment shall be listed as a complete assembly for use in Class I, Division 1 locations.
- 46
Areas where combustible dust is normally in air sufficient to produce explosive mixtures are:
Explanation
NEC 500.5(C)(1): Class II, Division 1 is where combustible dust is in the air under normal operating conditions in quantities sufficient to produce explosive mixtures.
- 47
Class II, Division 2 is where combustible dust in the air is:
Explanation
NEC 500.5(C)(2): Class II, Division 2 is where combustible dust is not normally in air in sufficient quantities, but accumulations may occur on equipment.
- 48
MC-HL cables in Class I, Division 1 must be sealed at:
Explanation
NEC 501.15(D)(1): Cables like Type MC-HL shall be sealed with listed fitting after removing jacket so sealing compound surrounds each individual insulated conductor.
- 49
Marina main overcurrent protection must have GFPE not exceeding:
Explanation
NEC 555.35(A)(1): The main overcurrent protective device feeding a marina shall have ground-fault protection of equipment not exceeding 30 mA.
- 50
In corrosive agricultural buildings, which wiring method cannot be used unprotected?
Explanation
NEC 547.5(A) and 344.10: Plain RMC without supplementary corrosion protection rapidly corrodes in agricultural atmospheres (ammonia, moisture). Approved methods are non-metallic (PVC, UF, NMC) or specially protected metals.