Topic 08 · Motors & Controllers
Set A Questions 1 to 10
- 1
When calculating ampacity for conductors supplying a single continuous-duty motor, what percentage of full-load current is required?
Explanation
NEC 430.22: Conductors supplying a single continuous-duty motor must have an ampacity of not less than 125 percent of the motor full-load current rating.
- 2
Where should you find the FLC used for sizing motor circuit conductors and switches?
Explanation
NEC 430.6(A)(1): Values in Tables 430.247 through 430.250 must be used to determine conductor ampacity and switch ratings instead of the motor nameplate current.
- 3
When is the motor nameplate current used for design purposes?
Explanation
NEC 430.6(A)(2): Separate motor overload protection must be based on the motor nameplate current rating, not the NEC tables.
- 4
Feeder conductors for two or more motors must have ampacity of 125% of the highest motor FLC plus what?
Explanation
NEC 430.24: Feeder conductors must have ampacity of 125% of the highest-rated motor full-load current rating plus the sum of the full-load current ratings of all other motors.
- 5
What is the maximum percent setting for an inverse time breaker protecting a typical squirrel-cage motor?
Explanation
NEC Table 430.52: For AC polyphase squirrel-cage motors, the maximum setting for an inverse time circuit breaker is 250% of the full-load current.
- 6
If calculated motor protection does not match a standard device size, you shall use:
Explanation
NEC 430.52(C)(1) Exception 1: Where calculated values do not correspond to standard sizes, the next higher standard size or setting is permitted.
- 7
For an instantaneous trip breaker on a squirrel-cage motor, Table 430.52 permits a maximum of:
Explanation
NEC Table 430.52: Maximum instantaneous trip for squirrel-cage motors is 800%. Exception 1 allows up to 1300% if 800% is insufficient for starting current.
- 8
According to NEC Table 430.250, what is the FLC for a 10 HP, 3-phase, 460V motor?
Explanation
NEC Table 430.250: The full-load current for a 10 HP, 460V, 3-phase motor is 14 amperes.
- 9
For a single 10 HP, 3-phase, 460V continuous motor, calculate minimum conductor ampacity needed:
Explanation
NEC 430.22: FLC from Table 430.250 is 14A. Required ampacity = 14A × 125% = 17.5 amperes.
- 10
For a motor with SF 1.15, what is the maximum overload relay setting?
Explanation
NEC 430.32(A)(1): Motors with service factor 1.15 or greater are protected by overload devices set to trip at not more than 125% of nameplate FLC.