Topic 08 · Motors & Controllers
Set B Questions 11 to 20
- 11
Motors with temperature rise ≤40°C may have overload protection set to:
Explanation
NEC 430.32(A)(1): Motors marked with temperature rise of 40°C or less are protected by overload devices set to not more than 125% of full-load current rating.
- 12
Standard motors (SF 1.0, not otherwise marked) require overload protection at:
Explanation
NEC 430.32(A)(1): All other motors are protected with overload devices not exceeding 115% of the motor nameplate full-load current rating.
- 13
If a standard overload relay cannot start a 1.15 SF motor, the maximum allowed is:
Explanation
NEC 430.32(C): Where the selected overload relay is insufficient to start the motor, the next higher size is permitted, not to exceed 140% trip current for 1.15 SF motors.
- 14
A motor disconnecting means must be located:
Explanation
NEC 430.102(B)(1): A disconnecting means must be located in sight from both the motor location and the driven machinery location.
- 15
What does "in sight from" mean per Article 100 of the NEC?
Explanation
NEC Article 100: Where equipment must be "in sight from" another, the specified equipment must be visible and not more than 15 m (50 feet) distant.
- 16
When may the motor disconnect NOT be in sight of the motor?
Explanation
NEC 430.102(B)(2) Exception: In hazardous locations or industrial installations, disconnect need not be in sight if individually capable of being locked in open position with locking provision remaining in place.
- 17
A motor disconnecting means ampere rating must be not less than:
Explanation
NEC 430.110(A): The disconnecting means for motors at 1000 volts or less must have an ampere rating not less than 115 percent of the motor full-load current.
- 18
Besides ampere rating, a motor disconnect must be:
Explanation
NEC 430.109(A)(1): The disconnecting means must generally be a horsepower-rated motor-circuit switch or a circuit breaker, with limited exceptions for general-use switches.
- 19
A general-use snap switch may disconnect motors rated _____ or less at 300V or less if rated twice the FLC:
Explanation
NEC 430.109(C)(1): For stationary motors 2 hp or less at 300 volts or less, a general-use switch with ampere rating at least twice the motor FLC is permitted.
- 20
A motor controller must have a horsepower rating:
Explanation
NEC 430.83(A): The controller must have a horsepower rating at the application voltage not lower than the horsepower rating of the motor.