Topic 08 · Motors & Controllers
Set C Questions 21 to 30
- 21
According to Table 430.250, the FLC for a 5 HP, 3-phase, 208V motor is:
Explanation
NEC Table 430.250: A 5 HP, 3-phase, 208V motor has a full-load current of 16.7 amperes.
- 22
For a 5 HP, 208V, 3-phase motor, maximum non-time-delay fuse size by Table 430.52?
Explanation
NEC Table 430.52: FLC 16.7A × 300% max = 50.1A. Exception 1 of 430.52(C) permits next standard size above calculated value, which is 60A.
- 23
For a 5 HP, 208V motor, maximum dual-element (time-delay) fuse size?
Explanation
NEC Table 430.52: FLC 16.7A × 175% max = 29.2A. Next standard fuse size per 240.6 not exceeding this is 30A.
- 24
A continuous-duty motor with nameplate 10A FLC and 1.15 SF: maximum overload setting?
Explanation
NEC 430.32(A)(1): Motors with 1.15 service factor allow overload settings of 125% maximum. 10A × 125% = 12.5 amperes.
- 25
Feeder short-circuit protection for multiple motors is calculated by adding:
Explanation
NEC 430.62(A): Feeder protection is limited to not more than the largest branch-circuit device rating for any motor plus the sum of full-load currents of other motors.
- 26
Feeder for 10 HP (14A with 35A breaker), 5 HP (7.6A), 3 HP (4.8A) @ 460V: max feeder breaker?
Explanation
NEC 430.62(A): Max feeder protection = largest branch device (35A) + other motor FLC (7.6 + 4.8 = 12.4A) = 47.4A. Use next lower standard size: 45A.
- 27
A motor control circuit is the circuit that:
Explanation
NEC 430.71: A motor control circuit carries the electric signals directing the controller performance but does not carry the main power current.
- 28
Motor control circuit taps inside the controller enclosure need separate protection only if:
Explanation
NEC 430.72(A): Control circuit taps from load side inside the enclosure can rely on the branch-circuit protective device for protection under specified conditions.
- 29
When one controller serves a motor and electric heater, its rating must be:
Explanation
NEC 430.83(B): Controllers for mixed loads must have a rating not less than the combined load as determined by Article 220.
- 30
A cord-and-plug motor rated _____ or less may use attachment plug as controller:
Explanation
NEC 430.81(B): A portable motor rated 1/3 horsepower or less may use an attachment plug and receptacle as the controller.