Topic 08 · Motors & Controllers
Set D Questions 31 to 40
- 31
For a cord-and-plug-connected motor, the disconnecting means may be:
Explanation
NEC 430.109(F): For cord-and-plug-connected motors, a horsepower-rated attachment plug and receptacle with proper ratings serves as the disconnecting means.
- 32
If motor and controller are not in sight of each other, the disconnect must be:
Explanation
NEC 430.102(A) Exception 1: Where disconnect is not in sight of controller location, it must be individually capable of being locked in the open position with locking provision remaining in place.
- 33
For a stationary motor with FLC not exceeding 2 amps, the disconnect may be:
Explanation
NEC 430.109(C): A general AC snap switch if motor FLC does not exceed 80% of switch rating, OR a general-use switch with rating at least twice the motor FLC.
- 34
According to NEC Table 430.248, what is the FLC for a single-phase, 115V, 1 HP motor?
Explanation
NEC Table 430.248: Full-load current for a 1 HP, single-phase, 115V motor is 16 amperes.
- 35
For a single-phase, 230V, 2 HP continuous motor, calculate minimum conductor ampacity:
Explanation
NEC Table 430.248: 2 HP, 230V FLC = 12A. NEC 430.22 requires 125% ampacity: 12A × 1.25 = 15 amperes.
- 36
Can a single-motor branch circuit supply lighting loads?
Explanation
NEC 210.23(A): Utilization equipment other than luminaires may not exceed 50% of branch-circuit rating when luminaires or equipment are also supplied on the same circuit.
- 37
A wound-rotor motor is an AC motor whose speed is controlled by:
Explanation
A wound-rotor (slip-ring) motor allows external resistance insertion in the rotor circuit via slip rings for speed and torque control, referenced separately in Table 430.52.
- 38
For a wound-rotor motor, the maximum inverse time breaker setting is:
Explanation
NEC Table 430.52: Wound-rotor AC motors are limited to 150% maximum for inverse time circuit breaker protection, lower than squirrel-cage motors.
- 39
When feeder supplies multiple motors at different speeds, conductor sizing is based on:
Explanation
NEC 430.24: Feeder conductors are calculated using 125% of the highest-rated motor FLC plus sum of other motors, regardless of individual speed variations.
- 40
For a multi-speed motor, branch conductors are sized on which current?
Explanation
NEC 430.22(B): Branch-circuit conductors for multi-speed motors must be based on the highest full-load current rating shown on the motor nameplate.