Topic 08 · Motors & Controllers
Set E Questions 41 to 50
- 41
A part-winding motor is an induction motor with:
Explanation
NEC 430.4: Part-winding motors have two or more separate star/delta windings energized sequentially to reduce starting current.
- 42
When separate circuits supply a part-winding motor, each circuit ampacity must be:
Explanation
NEC 430.22(D): Each separate branch circuit for a part-winding motor shall have ampacity not less than one-half of the full-load current required by 430.22 for each winding.
- 43
Live motor parts operating 50-1000V must be guarded by:
Explanation
NEC 430.232: Live motor parts operating 50 volts or more must be guarded against accidental contact by enclosure, elevation of 8 feet or more, or room access limited to qualified persons.
- 44
In Class II Division 1 (combustible dust), motors must be:
Explanation
NEC 502.125(A): In Class II Division 1 locations, motors must be identified for the location or totally enclosed pipe-ventilated, totally enclosed water-cooled, etc.
- 45
Must a motor controller open all ungrounded conductors?
Explanation
NEC 430.84: A controller is not required to open all conductors. Exception: When the controller also serves as the disconnecting means, it must open all ungrounded conductors per 430.111.
- 46
For a 60A branch-circuit breaker motor circuit, EGC size from Table 250.122 is:
Explanation
NEC Table 250.122: Equipment grounding conductor size is determined by the overcurrent device rating. A 60A device requires 10 AWG copper EGC.
- 47
For wound-rotor secondary conductors between motor and controller, continuous-duty ampacity must be:
Explanation
NEC 430.23(A): Secondary conductors on wound-rotor motors must have ampacity not less than 125 percent of the full-load secondary current for continuous duty.
- 48
Motor overload devices are intended to protect against:
Explanation
NEC 430.31: Overload protection prevents excessive heating from motor overloads and failure to start. Short-circuit/ground-fault protection is separate.
- 49
An integral thermal protector for a motor with ≤40°C rise must trip at maximum:
Explanation
NEC 430.32(A)(2): Integral thermal protectors on motors ≤40°C rise with FLC 9.0A or less trip at maximum 170% of full-load current.
- 50
NEMA Design B on a motor nameplate indicates:
Explanation
NEMA Design B is the standard AC induction motor with normal starting torque, normal starting current, and low slip. NEC acknowledges this in Table 430.251(B).