Topic 04 · Overcurrent Protection
Set A Questions 1 to 10
- 1
Which is NOT a standard ampere rating for overcurrent devices per NEC 240.6(A)?
Explanation
NEC 240.6(A): Standard ratings are 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125... Note: 55 A is not a standard rating.
- 2
When conductor ampacity does not match a standard device rating, the next higher rating is permitted only if it does not exceed:
Explanation
NEC 240.4(B): For devices rated 800 amperes or less, the next higher standard overcurrent device rating shall not exceed 800 amperes.
- 3
What must the conductor ampacity be for overcurrent devices rated over 800 amperes?
Explanation
NEC 240.4(C): Where the overcurrent device is rated over 800 amperes, the ampacity of conductors it protects shall be equal to or greater than the device rating.
- 4
What is the maximum overcurrent protection for 12 AWG copper?
Explanation
NEC 240.4(D)(5): The overcurrent protection shall not exceed 20 amperes for 12 AWG copper conductors.
- 5
The highest position of a circuit breaker handle shall not exceed what height?
Explanation
NEC 240.24(A): The center of the grip of the operating handle, when in its highest position, shall not be more than 2.0 m (6 ft 7 in.) above the floor.
- 6
Overcurrent devices CANNOT be installed in which location?
Explanation
NEC 240.24(D): Overcurrent devices shall not be located in the vicinity of easily ignitable material such as in clothes closets.
- 7
In dwelling units, overcurrent devices shall NOT be installed in:
Explanation
NEC 240.24(E): In dwelling units, overcurrent devices shall not be located in bathrooms.
- 8
A 10-foot feeder tap is permitted without overcurrent protection if ampacity meets:
Explanation
NEC 240.21(B)(1): Tap conductors must meet all three: calculated load, device rating, and not less than 1/10 of feeder OCPD rating.
- 9
For a 25-foot feeder tap, ampacity must be at least:
Explanation
NEC 240.21(B)(2): Tap conductors not over 7.5 m (25 ft) must have ampacity not less than one-third of the feeder OCPD rating.
- 10
When a circuit breaker handle is vertical, the "up" position means:
Explanation
NEC 240.81: Where circuit breaker handles are operated vertically, the "up" position of the handle shall be the "on" position.