Topic 04 · Overcurrent Protection
Set B Questions 11 to 20
- 11
Edison-base fuses are permitted for replacements only if:
Explanation
NEC 240.51(B): Edison-base plug fuses shall be used only for replacements in existing installations where there is no evidence of overfusing or tampering.
- 12
Type S plug fuses prevent:
Explanation
NEC 240.53(B): Type S designs make it difficult to insert a fuse of any given class into a fuseholder designed for a different current rating.
- 13
Plug fuses and fuseholders shall not be used above:
Explanation
NEC 240.50(A): Plug fuses shall not be used in circuits exceeding 125 volts between conductors, unless on a grounded neutral system with no conductor over 150 V to ground.
- 14
What is the maximum rating for an Edison-base plug fuse?
Explanation
NEC 240.50(A) and 240.51(A): Plug fuses shall be classified at not over 125 volts and 30 amperes and below.
- 15
Circuit breaker ampere ratings must be marked on:
Explanation
NEC 240.83(B): Circuit breakers 100 A or less shall have ampere ratings molded, stamped, etched, or marked into the handle or escutcheon area.
- 16
A circuit breaker's interrupting rating must be marked if it differs from:
Explanation
NEC 240.83(C): Every circuit breaker having an interrupting rating other than 5,000 amperes shall have its interrupting rating shown on the breaker.
- 17
Fuses must be plainly marked with:
Explanation
NEC 240.60(C): Fuses shall show ampere rating, voltage rating, interrupting rating (if other than 10,000 A), and manufacturer information.
- 18
Conductors shall be protected against overcurrent based on their:
Explanation
NEC 240.4: Conductors shall be protected against overcurrent in accordance with their ampacities specified in 310.14.
- 19
An overcurrent device in a grounded conductor is allowed if:
Explanation
NEC 240.22: No OCPD shall be connected in series with a grounded conductor unless it opens all conductors, with no independent operation.
- 20
Circuit breakers switching 120V/277V fluorescent circuits must be marked:
Explanation
NEC 240.83(D): Circuit breakers used to switch 120-volt and 277-volt fluorescent lighting circuits shall be listed and marked SWD or HID.