Topic 04 · Overcurrent Protection
Set C Questions 21 to 30
- 21
A ground-fault is an unintentional connection between:
Explanation
NEC Article 100: Ground Fault is an unintentional, electrically conductive connection between an ungrounded conductor and the normally non-current-carrying conductors, metallic enclosures, or earth.
- 22
A record of GFPE performance testing must be maintained by:
Explanation
NEC 230.95(C): A written record of GFPE testing shall be made and shall be available to the authority having jurisdiction.
- 23
AFCI protection is NOT required in dwelling unit:
Explanation
NEC 210.12(B): AFCI is required in kitchens, family rooms, bedrooms, living rooms and other areas, but generally not in bathrooms (which require GFCI).
- 24
New bedroom branch circuits must use:
Explanation
NEC 210.12(A)(1): A listed combination-type AFCI must protect the entire branch circuit, typically via an AFCI breaker.
- 25
Fuses and circuit breakers protect both short circuits and:
Explanation
OCPDs clear short circuits (faults) and overloads that exceed the ampacity rating and create excessive heat.
- 26
A 20A breaker on 14 AWG is permitted for motors when:
Explanation
NEC 240.4(G) and Article 430: Motor branch-circuit short-circuit protection can exceed conductor ampacity (e.g., 250% for inverse-time breaker) to allow motor starting.
- 27
Supplementary overcurrent protection is:
Explanation
NEC Article 100: Supplementary protection provides limited overcurrent protection for specific equipment components, supplementing branch-circuit OCPD protection.
- 28
An inverse-time circuit breaker means:
Explanation
NEC Article 100: Inverse time circuit breaker has a purposeful delay that decreases as overcurrent magnitude increases.
- 29
Equipment rated 800 A+ must be field-marked with:
Explanation
NEC 110.24(A): Service equipment shall be field-marked with maximum available fault current and the date the calculation was performed.
- 30
Cartridge fuses are classified by:
Explanation
NEC 240.60(A): Cartridge fuses and fuseholders shall be classified according to voltage and ampere ranges.