Topic 04 · Overcurrent Protection
Set D Questions 31 to 40
- 31
A current-limiting OCPD reduces fault current to:
Explanation
NEC 240.2: A current-limiting device reduces fault current to substantially less than obtainable with a solid conductor of comparable impedance.
- 32
A 10-foot generator tap ampacity must be at least:
Explanation
NEC 240.21(G): Tap conductors not over 10 ft must have ampacity not less than the rating of equipment containing the overcurrent devices supplied by the tap.
- 33
Fuses in locations accessible only to qualified persons MAY be unenclosed if they are on:
Explanation
NEC 240.30(A) Exception: Fuses on switchboards/control panels operating at not over 150 V to ground and accessible only to qualified persons need not be enclosed.
- 34
The lowest standard ampere rating for circuit breakers is:
Explanation
NEC 240.6(A): The standard ampere ratings include 15 as the lowest listed value for fuses and inverse-time circuit breakers.
- 35
Adjustable-trip breakers with restricted adjustment access are rated at:
Explanation
NEC 240.6(C): Restricted-access adjustable breakers may be rated at the adjusted (long-time pickup) setting, not the frame rating.
- 36
A 25-foot transformer secondary tap ampacity must equal:
Explanation
NEC 240.21(C)(2): Secondary conductor ampacity = (Primary-to-secondary voltage ratio) × (1/3 of primary OCPD rating).
- 37
A circuit breaker is defined as a device that:
Explanation
NEC Article 100: Circuit Breaker is designed to open/close by nonautomatic means and open automatically on predetermined overcurrent without damage.
- 38
Parallel OCPDs in the field are:
Explanation
NEC 240.8: Fuses and circuit breakers shall not be connected in parallel except when factory-assembled in parallel and listed as a unit.
- 39
Overcurrent devices in wet locations must be in:
Explanation
NEC 240.32: Enclosures for OCPDs in damp/wet locations must comply with 312.2(A), requiring weatherproof enclosures like Type 3R.
- 40
In a 120/240V single-phase service, ungrounded conductors must be:
Explanation
NEC 240.15(A): An overcurrent device shall be connected in series with each ungrounded conductor.