Topic 04 · Overcurrent Protection
Set E Questions 41 to 50
- 41
Single-pole breakers with handle ties for multiwire circuits supply:
Explanation
NEC 240.15(B): Single-pole breakers with ties for multiwire circuits permit line-to-neutral loads; simultaneous opening is required.
- 42
A panelboard breaker's interrupting rating must be:
Explanation
NEC 110.9: Equipment shall have an interrupting rating equal to or greater than the available current at the line terminals.
- 43
Eighteen AWG fixture wire with a 20A OCPD is permitted for:
Explanation
NEC 240.5(B)(2): 18 AWG fixture wire may be used up to 50 ft on 20A circuits when approved for specific listed appliances.
- 44
Fire pump motor short-circuit protection must:
Explanation
NEC 695.4(B)(2)(a): Fire pump OCPD shall be selected to carry indefinitely the locked-rotor current, prioritizing fire suppression over motor protection.
- 45
A motor overload device protects against:
Explanation
NEC 430.31: Motor overload protection guards against excessive heating due to overloads and failure to start, NOT faults.
- 46
A single 120V receptacle on an individual branch circuit must have a rating:
Explanation
NEC 210.21(B)(1): A single receptacle on an individual branch circuit shall have an ampere rating not less than the branch circuit.
- 47
Continuous load 40A + noncontinuous 20A requires minimum OCPD of:
Explanation
NEC 210.20(A): OCPD = 100% noncontinuous + 125% continuous = 20A + (40A × 1.25) = 70A (standard rating).
- 48
The minimum working space depth in front of a 120/240V panel is:
Explanation
NEC 110.26(A)(1): Minimum clear distance for 0–150V equipment is 900 mm (36 in. or 3 ft) measured from the front.
- 49
A 100A adjustable breaker with sealed access is rated at:
Explanation
NEC 240.6(C): Adjustable breakers with restricted access are rated at the actual adjusted (long-time pickup) setting for conductor sizing.
- 50
Arc energy reduction for breakers ≥1200A must reduce:
Explanation
NEC 240.87(B): Arc energy reduction means shall reduce the clearing time, lowering incident energy if an arc flash occurs during maintenance.