Set A Questions 1 to 10
- 1
According to NEC Article 100, what is the definition of "Service"?
Explanation
NEC Article 100: Service means the conductors and equipment connecting the electric utility to the wiring system of the premises served.
- 2
The point of connection between utility facilities and premises wiring is the:
Explanation
NEC Article 100: Service Point is the point of connection between the utilities supply facilities and the premises wiring.
- 3
Underground conductors between utility system and service point are called:
Explanation
NEC Article 100: Service Lateral is the underground conductors between the utility electric supply system and the service point.
- 4
Which installation typically permits a second service?
Explanation
NEC 230.2(A): Special Conditions permit additional services for fire pumps, emergency systems, legally required standby service, and optional standby systems.
- 5
By special permission, a second service may be installed for loads exceeding:
Explanation
NEC 230.2(C)(1): Additional services may be installed where capacity requirements exceed 2000 amperes at 1000 volts or less.
- 6
Service conductors must not pass through the interior of:
Explanation
NEC 230.3: Service conductors supplying a building shall not pass through the interior of another building or structure.
- 7
Minimum clearance of unjacketed service cable from windows is:
Explanation
NEC 230.9(A): Service conductors without outer jacket shall have clearance of not less than 900 mm (3 ft) from windows designed to be opened.
- 8
Above finished grade, minimum clearance of service drops is:
Explanation
NEC 230.24(B)(1): Service drops above pedestrian areas require 3.0 m (10 ft) clearance minimum where voltage not exceeds 150 V to ground.
- 9
Service-drop clearance over residential property (300V or less):
Explanation
NEC 230.24(B)(3): Over residential property and driveways, minimum clearance is 4.5 m (15 ft) where voltage not exceeds 300 V to ground.
- 10
Service-drop clearance over public streets and truck areas is:
Explanation
NEC 230.24(B)(4): Over public streets and areas subject to truck traffic requires 5.5 m (18 ft) minimum clearance.