Set B Questions 11 to 20
- 11
Minimum vertical clearance of service drops above roof is:
Explanation
NEC 230.24(A): Service-drop conductors shall have 2.5 m (8 ft) vertical clearance above the roof surface.
- 12
Steeper roof slope (4:12) allows service drop clearance reduction to:
Explanation
NEC 230.24(A) Exception 2: Where voltage not exceeds 300V and roof slope is 4 in 12 or greater, clearance reduces to 900 mm (3 ft).
- 13
Underground service conductors require adequate _____ strength:
Explanation
NEC 230.31(A): Underground service conductors must have sufficient ampacity and adequate mechanical strength.
- 14
Minimum size copper for underground service conductors:
Explanation
NEC 230.31(B): Conductors shall not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum.
- 15
Which wiring method is NOT approved for service conductors?
Explanation
NEC 230.43: FMC is limited to maximum 6 feet length; unlimited FMC not permitted for service-entrance conductors.
- 16
Service raceways must have a _____ at inner ends:
Explanation
NEC 230.50(B): Raceways containing service conductors shall be equipped with a bushing to protect conductors from abrasion.
- 17
Service heads must be located _____ service-drop attachment:
Explanation
NEC 230.54(C): Service heads shall be located above the point of attachment of service-drop conductors to the building.
- 18
To prevent water entry into service equipment, a _____ is required:
Explanation
NEC 230.54(F): Drip loops shall be formed on individual conductors to prevent water from entering service equipment.
- 19
Service disconnecting means location requirement is:
Explanation
NEC 230.70(A)(1): Service disconnecting means shall be at readily accessible location either outside or inside nearest the point of entrance of service conductors.
- 20
Maximum number of main disconnects for one service:
Explanation
NEC 230.71(B): a service may have up to six disconnecting means. Since the 2020 NEC each must be in its own enclosure (or its own section of a switchboard or switchgear), so six breakers in one panel no longer count.