Set C Questions 21 to 30
- 21
Multiple service disconnects must be:
Explanation
NEC 230.72(A): Two to six disconnects shall be grouped and each marked to indicate the load served.
- 22
Minimum rating for one-family dwelling service disconnect:
Explanation
NEC 230.79(C): For a one-family dwelling, service disconnecting means rating shall not be less than 100 amperes, 3-wire.
- 23
Service overcurrent protection device location relative to disconnect:
Explanation
NEC 230.91: Service overcurrent device shall be integral part of disconnect means or located immediately adjacent thereto.
- 24
GFPE required for grounded wye services 150V-1000V at ratings of:
Explanation
NEC 230.95: Ground-fault protection for services over 150V to ground requires GFPE at each service disconnect rated 1000 amperes or more.
- 25
The grounded conductor in a feeder is often called the:
Explanation
NEC Article 100: The Neutral Conductor is a grounded conductor carrying neutral current between ungrounded conductors.
- 26
Feeder conductor sizing is determined by:
Explanation
NEC 215.2(A)(1): Feeder conductor size shall be based on calculated load per Article 220.
- 27
Feeder ampacity for continuous loads requires:
Explanation
NEC 215.2(A)(1)(a): Feeder ampacity shall be not less than 125 percent of the continuous load plus 100 percent of noncontinuous load.
- 28
Feeders supplying branch circuits require equipment grounding when:
Explanation
NEC 215.6: Equipment grounding conductor required in feeder when branch circuits require grounding conductors per 250.134.
- 29
Feeder overcurrent device rating for continuous loads:
Explanation
NEC 215.3: Overcurrent device rating not less than noncontinuous load plus 125 percent of continuous load.
- 30
All feeder conductors in one metal raceway must achieve:
Explanation
NEC 300.3(B): All circuit conductors and equipment grounding conductors shall be in same raceway to prevent induction heating.