Set E Questions 41 to 50
- 41
Demand factor 75% applies to four or more _____ in dwellings:
Explanation
NEC 220.53: 75% demand factor permitted for four or more fixed appliances (excluding ranges, dryers, heating, AC).
- 42
Underground service warning ribbon depth requirement:
Explanation
NEC 300.5(D)(3): Warning ribbon for buried conductors minimum 18 in. deep shall be placed 300 mm (12 in.) above installation.
- 43
Service equipment in wet location must be:
Explanation
NEC 312.2: Wet location enclosures require weatherproof (NEMA 3R) protection with 1/4-inch airspace from wall.
- 44
Service disconnect handle must show:
Explanation
NEC 230.77: Service disconnecting means shall plainly indicate whether in the open or closed position.
- 45
Single-family dwelling minimum service rating is typically:
Explanation
NEC 230.79(C): One-family dwelling service disconnecting means rating not less than 100 amperes, 3-wire.
- 46
Metal underground water pipe grounding electrode requirement:
Explanation
NEC 250.52(A)(1): Metal underground water pipe in direct earth contact minimum 3.0 m (10 ft) as grounding electrode.
- 47
Separately Derived System power source excludes:
Explanation
NEC Article 100: Separately Derived System is power from source other than the service.
- 48
Feeder neutral conductor size reduction basis:
Explanation
NEC 220.61(A): Feeder neutral sized for maximum unbalance as determined by Article 220 requirements.
- 49
Which load prohibits demand factor on neutral?
Explanation
NEC 220.61(C): No reduction permitted for nonlinear loads from 4-wire wye systems due to triplen harmonics.
- 50
Service mast support requirement for service drops:
Explanation
NEC 230.28: Service mast must be adequate strength or supported by braces or guys to safely withstand service drop strain.