Topic 10 · Special Occupancies
Set A Questions 1 to 10
- 1
What wiring method is required for life safety and critical branches in healthcare facility EES installations?
Explanation
NEC 517.31(C)(3) requires nonflexible metal raceways, Type MI cable, or Schedule 80 PVC (under specific conditions) for essential electrical system branches in healthcare facilities.
- 2
Patient care receptacles need what grounding arrangement?
Explanation
NEC 517.13(A) & (B): Redundant grounding with both an insulated copper EGC and a metal raceway qualifying as grounding return path is required for patient care vicinity receptacles.
- 3
Hospital patient care receptacles require which marking?
Explanation
NEC 517.18(B) mandates that receptacles in patient care vicinities be marked as "Hospital Grade" receptacles, typically with a green dot on the faceplate.
- 4
For assembly occupancies (100+ persons), is Type NM cable permitted?
Explanation
NEC 518.4(A) prohibits nonmetallic-sheathed cable for rated fire-resistive construction in assembly occupancies designed for 100 or more persons.
- 5
At carnivals/fairs, overhead drops above pedestrian areas need minimum clearance of:
Explanation
NEC 525.5(B)(1) requires a minimum clearance of 3.0 m (10 ft) above areas accessible to pedestrians for overhead drop cords.
- 6
Portable distribution boxes at fairs must be elevated above ground by:
Explanation
NEC 525.22(A) requires portable distribution and termination boxes to be elevated above the ground not less than 150 mm (6 in.).
- 7
Receptacles accessible to the general public at a carnival require what protection?
Explanation
NEC 525.23(A) requires GFCI protection for all 125-volt, single-phase, 15- and 20-ampere non-locking receptacles that are readily accessible to the general public.
- 8
Agricultural buildings present hazards from excessive dust and corrosive conditions. Which wiring methods are acceptable?
Explanation
NEC 547.1(A) and 547.4 address corrosive atmospheres and excessive dust in agricultural buildings, requiring metallic raceways or Type MC cable for protection.
- 9
An equipotential plane in livestock areas reduces which hazard?
Explanation
NEC 547.2 and 547.10 establish an equipotential plane to mitigate step and touch voltages in livestock areas, as animals are highly sensitive to stray voltage.
- 10
Mobile home service cords are rated for minimum:
Explanation
NEC 550.10(A) specifies the mobile home power-supply cord shall be rated at 50 amperes.