Mobile home service equipment location distance limit:
Explanation
NEC 550.32(A) mandates service equipment be located in sight from and not more than 9.0 m (30 ft) from the mobile homes exterior wall.
- 12
New RV park sites with electrical supply must have 50-ampere receptacles at what minimum percentage?
Explanation
NEC 551.71(C) requires at least 40% of all new recreational vehicle sites with electrical supply to have a 50-ampere, 125/250-volt receptacle (20% is still enough at existing sites).
- 13
For a 100-site RV park, how many 30-ampere receptacles minimum?
Explanation
NEC 551.71(B) mandates a minimum of 70% of recreational vehicle sites with electrical supply have a 30-ampere, 125-volt receptacle.
- 14
Marina main overcurrent device ground-fault setting cannot exceed:
Explanation
NEC 555.35(A)(1) limits the main overcurrent protective device ground-fault protection to not exceeding 30 mA for marinas and boatyards.
- 15
Shore power receptacles require ground-fault protection of:
Explanation
NEC 555.35(A)(3) requires receptacles providing shore power to have ground-fault protection not exceeding 30 mA.
- 16
For floating piers, the electrical datum plane is located:
Explanation
NEC 555.2 defines the electrical datum plane as a horizontal plane 762 mm (30 in.) above the water level at floating piers.
- 17
Covered cables over pools require clearance to water of:
Explanation
NEC Table 680.9(A) specifies 22.5 feet (6.9 m) minimum clearance in any direction to water level for insulated cables at 0-750V.
- 18
Underground wiring is not permitted within ___ of a pools inside wall:
Explanation
NEC 680.11 prohibits underground wiring within 1.5 m (5 ft) horizontally from the inside wall of an in-ground pool, except for pool equipment supply.
- 19
Pool receptacles must be located between ___ and ___ from pool wall:
Explanation
NEC 680.22(A)(1) requires receptacles not less than 1.83 m (6 ft) and not more than 6.0 m (20 ft) from the pools inside wall.
- 20
GFCI protection applies to receptacles within ___ of pool wall:
Explanation
NEC 680.22(A)(4) requires GFCI protection for all 15- and 20-ampere, single-phase, 125-volt receptacles within 6.0 m (20 ft) of pool walls.