Topic 10 · Special Occupancies
Set D Questions 31 to 40
- 31
One- or two-family dwelling PV systems limited to maximum:
Explanation
NEC 690.7 specifies the maximum PV system voltage for one- and two-family dwellings shall be 600 volts.
- 32
PV rapid shutdown must reduce outside array conductor voltage to within:
Explanation
NEC 690.12(B)(1) requires controlled conductors outside the array boundary to be limited to not more than 30 volts within 30 seconds of rapid shutdown.
- 33
PV system disconnects are prohibited in:
Explanation
NEC 690.13(A) prohibits PV system disconnecting means from being installed in bathrooms.
- 34
Emergency Systems (Article 700) must provide power within maximum:
Explanation
NEC 700.12 requires emergency lighting and power be available within 10 seconds upon normal supply failure.
- 35
Emergency system wiring must be kept independent from all other wiring to:
Explanation
NEC 700.10(B) mandates emergency circuit wiring be completely independent from all other wiring and equipment to ensure system integrity.
- 36
Legally Required Standby Systems (Article 701) available within:
Explanation
NEC 701.12 specifies legally required standby power must be available within 60 seconds of normal supply failure.
- 37
Optional Standby Systems differ from Emergency Systems in that they:
Explanation
NEC Article 702 covers Optional Standby Systems (like residential backup generators) without imposing maximum time limits for power restoration.
- 38
Information Technology Equipment room under-floor power cables require:
Explanation
NEC 645.5(E) permits specific wiring methods like Type DP cable, metal conduits, or MC cable under raised floors in IT equipment rooms.
- 39
IT Equipment room emergency disconnect must deactivate:
Explanation
NEC 645.10 requires approved means to disconnect power to all electronic equipment AND dedicated HVAC systems serving the IT room.
- 40
Sign disconnecting means (Article 600) location requirement:
Explanation
NEC 600.6(A) requires the disconnect within sight of the sign, or if remote, capable of being locked in the open position.