Topic 10 · Special Occupancies
Set E Questions 41 to 50
- 41
Elevator machine room lighting switch must be at:
Explanation
NEC 620.23(A) requires the machine room lighting switch be located at the point of entry to provide convenient control.
- 42
Elevator disconnecting means location must be:
Explanation
NEC 620.51(C) requires the disconnect be readily accessible to qualified persons in the machine room, within sight of motor controller.
- 43
Electric Vehicle Supply Equipment (EVSE) cable maximum length without management system:
Explanation
NEC 625.17(A) limits overall usable EVSE cable length to 7.5 m (25 ft) unless equipped with a cable management system.
- 44
EV charging stations require personnel shock protection via:
Explanation
NEC 625.22 mandates electric vehicle supply equipment have a listed protection system against electrical shock of personnel.
- 45
Manufactured home lighting load is calculated at ___ per square foot:
Explanation
NEC 550.18(A) specifies lighting load calculation on the basis of 33 volt-amperes/m² (3 VA/ft²) for manufactured homes.
- 46
Fire pump motor overcurrent protective device must carry locked-rotor current:
Explanation
NEC 695.4(B)(2)(1) requires overcurrent devices carry the sum of locked-rotor currents indefinitely to ensure pump operation during fire.
- 47
Fire pump branch circuit wiring in exposed areas uses:
Explanation
NEC 695.6(D) requires rigid metal conduit, intermediate metal conduit, or Type MI cable for fire pump branch circuits subject to physical damage.
- 48
Receptacles in elevator pits require:
Explanation
NEC 620.85 mandates GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles in pits and hoistways.
- 49
Healthcare facility branch circuits use Type MI or:
Explanation
NEC 517.31(C)(3) requires nonflexible metal raceways or Type MI cable for healthcare facility life safety and critical branches.
- 50
Agricultural building equipotential plane protects livestock from stray:
Explanation
NEC 547.10 establishes equipotential planes to mitigate step and touch voltage hazards in livestock areas where animals are voltage-sensitive.