Topic 06 · Wiring Methods & Materials
Set B Questions 11 to 20
- 11
Which wiring method is NOT permitted in wet locations:
Explanation
NEC 334.12(B)(4): Nonmetallic-Sheathed Cable (Type NM) shall not be used in wet or damp locations.
- 12
Minimum concrete cover for raceway in solid rock:
Explanation
NEC 300.5 Table, Note 5: Where solid rock prevents compliance with cover requirements, wiring shall be in raceway and covered with at least 2 inches of concrete extending to the rock.
- 13
Conductor protection from abrasion entering enclosures:
Explanation
NEC 312.5(A): Conductors entering enclosures must be protected from abrasion with a fitting providing a smooth, rounded insulating surface (bushing).
- 14
Type MC cable support spacing maximum:
Explanation
NEC 330.30(B): Type MC cable shall be supported and secured at intervals not exceeding 6 feet.
- 15
Type MC cable spacing from box or termination:
Explanation
NEC 330.30(B): Cables containing four or fewer conductors no larger than 10 AWG shall be secured within 12 inches of every box.
- 16
Type NM cable support spacing and box distance:
Explanation
NEC 334.30: Type NM shall be supported and secured at 4.5-foot intervals maximum and within 12 inches of every outlet, junction box, cabinet, or fitting.
- 17
Type NM cable through bored holes is considered supported by:
Explanation
NEC 334.30(A): Cable passed through framing members is considered supported and secured by the structural framing itself.
- 18
Can Type NM cable be used as service-entrance:
Explanation
NEC 334.12: Types NM and NMC cables shall not be used as service-entrance cable.
- 19
Maximum quarter bends in single EMT run:
Explanation
NEC 358.26: There shall not be more than four quarter bends (360 degrees total) between pull points such as boxes and conduit bodies.
- 20
EMT support spacing requirement:
Explanation
NEC 358.30(A): EMT shall be securely fastened in place at least every 10 feet.