Topic 06 · Wiring Methods & Materials
Set C Questions 21 to 30
- 21
EMT spacing from box termination:
Explanation
NEC 358.30(A): EMT shall be securely fastened within 3 feet of each outlet, junction, box, or other termination.
- 22
ENT can be installed exposed in buildings exceeding three floors if:
Explanation
NEC 362.10: ENT in buildings exceeding three floors above grade must be concealed within walls, floors, and ceilings with a 15-minute fire-resistance barrier.
- 23
PVC conduit thermal expansion compensation threshold:
Explanation
NEC 352.44: Expansion fittings for PVC conduit shall be provided when length change is expected to be 1/4 inch or greater per straight run.
- 24
PVC conduit spacing from box:
Explanation
NEC 352.30(A): PVC conduit shall be securely fastened within 3 feet of each outlet, junction, device box, or conduit termination.
- 25
Maximum trade size for FMC:
Explanation
NEC 348.20(B): FMC larger than 4 inches (metric designator 103) shall not be used.
- 26
FMC as equipment grounding conductor acceptable when:
Explanation
NEC 250.118(5): FMC may serve as EGC when combined path length does not exceed 6 feet, circuit is 20A or less (3/8-1/2 in), and listed fittings are used.
- 27
Minimum trade size for LFMC:
Explanation
NEC 350.20(A): LFMC smaller than 3/8 inch (metric designator 12) shall not be used.
- 28
Volume of 4x4x1.5 inch square metal box:
Explanation
NEC Table 314.16(A): A 4x4x1-1/2 inch square box has an interior volume of 21.0 cubic inches.
- 29
Volume allowance for 12 AWG conductor:
Explanation
NEC Table 314.16(B): Each 12 AWG conductor requires 2.25 cubic inches of volume allowance in the box.
- 30
Duplex receptacle in box counts as how many conductors:
Explanation
NEC 314.16(B)(4): A device yoke with one or more devices counts as double volume allowance based on the largest conductor connected to it.