Topic 06 · Wiring Methods & Materials
Set E Questions 41 to 50
- 41
Different voltage systems in same raceway require:
Explanation
NEC 300.3(C)(1): All conductors must have insulation rated for the maximum circuit voltage applied to any conductor in the enclosure.
- 42
Single insulated conductors in cable tray allowed when:
Explanation
NEC 392.10(B)(1): Single-conductor cables 1/0 AWG and larger are permitted in industrial establishments with qualified maintenance.
- 43
Conductors exposed to sunlight must be:
Explanation
NEC 310.10(D): Conductors exposed to direct sunlight shall be listed or marked as sunlight resistant.
- 44
Ampacity derating begins when conductors in raceway exceed:
Explanation
NEC 310.15(C)(1): Ampacity adjustment factors apply when more than three current-carrying conductors are in a raceway or cable.
- 45
Adjustment factor for 4-6 current-carrying conductors:
Explanation
NEC Table 310.15(C)(1): When 4 to 6 current-carrying conductors are in a raceway, the adjustment factor is 80%.
- 46
Underground metallic raceway corrosion protection required when:
Explanation
NEC 300.6(A): Underground metallic raceways shall have protective coating where subject to severe corrosive influences.
- 47
Surface raceways not permitted where:
Explanation
NEC 386.12(1) and 388.12(1): Surface metal and nonmetallic raceways shall not be used where subject to severe physical damage.
- 48
Grounded conductor 6 AWG and smaller identification:
Explanation
NEC 200.6(A): Grounded conductors 6 AWG or smaller must have a continuous white or gray outer finish along their entire length.
- 49
High-leg color in 120/240V 3-phase delta system:
Explanation
NEC 110.15: The conductor with higher phase voltage to ground on 4-wire delta systems shall be permanently marked orange.
- 50
Busway support spacing requirement:
Explanation
NEC 368.30: Busways shall be securely supported at intervals not exceeding 5 feet unless otherwise designed and marked.