Topic 02 · General Regulations
Set B Questions 11 to 20
- 11
During backfilling, the first layer of backfill over the pipe shall be placed in layers not exceeding ____ thick.
Explanation
IPC 306.3: Backfill shall be firmly tamped in place in layers not exceeding 6 inches in depth.
- 12
A pipe sleeve must be at least ____ larger than the pipe.
Explanation
IPC 305.3: Sleeves must be at least two pipe sizes greater than the pipe passing through them.
- 13
Fire-rated assembly penetrations need:
Explanation
IPC 315.1: Fire-rated assemblies need approved firestop system per IBC.
- 14
Toilet rooms must be per IPC and:
Explanation
IPC 310.1: Toilet rooms must be per IBC and International Mechanical Code.
- 15
Toilet facilities for construction workers must be located no further than ____ from the working area.
Explanation
IPC 311.1: Toilet facilities for workers shall be located within a maximum of 500 feet from the place of work.
- 16
A water test applied to a drainage and vent system must be applied with a minimum water head of:
Explanation
IPC 312.2: A DWV water test shall be applied to the plumbing system entirely or in sections with not less than a 10-foot head of water.
- 17
How long must a water test be held upon a drainage system to pass inspection?
Explanation
IPC 312.2: The water shall be kept in the system, or in the portion under test, for at least 15 minutes before inspection starts.
- 18
If conducting an air test on the drainage and vent system, what is the required minimum pressure?
Explanation
IPC 312.3: An air test for DWV shall be made by forcing air into the system until there is a uniform gauge pressure of 5 psi.
- 19
For how long must the 5 psi air test for drainage and venting be maintained without introducing additional air?
Explanation
IPC 312.3: The air pressure must be held without introduction of additional air for a period of not less than 15 minutes.
- 20
Which piping material is explicitly prohibited by IPC from being tested with compressed air?
Explanation
IPC 312.3 (exception): Plastic pipe (PVC or ABS) shall not be tested with air due to the risk of uncontrolled fragmentation if a failure occurs.