Topic 02 · General Regulations
Set C Questions 21 to 30
- 21
The final plumbing test for a DWV system involves a visual inspection and, if required by the official, a:
Explanation
IPC 312.4: The final test shall be visual and, where required, a smoke or peppermint test to ensure gas and water tightness.
- 22
In a smoke test, what pressure must be introduced and maintained in the system?
Explanation
IPC 312.4.1: The smoke shall be introduced until a pressure of 1 inch water column is built up and maintained for 15 minutes.
- 23
In a peppermint test, how many ounces of oil of peppermint are required per 10 feet of stack height?
Explanation
IPC 312.4.2: Introduce 2 ounces of oil of peppermint into each line or stack for the odor test.
- 24
Water supply systems must test to:
Explanation
IPC 312.5: Test at working pressure or 50 psi air minimum.
- 25
Gravity sewer pipes test requires:
Explanation
IPC 312.6: Gravity sewer test is 10-foot water head or 5 psi air for 15 minutes.
- 26
Pipes through concrete walls require:
Explanation
IPC 305.1: Pipes through concrete/masonry need a sleeve or protective wrapping.
- 27
Rooms without windows need:
Explanation
IPC 310.1: Rooms need illumination and mechanical exhaust if no natural light or air.
- 28
V-Zone plumbing must resist:
Explanation
IPC 309.2: V-Zone systems must resist flotation, collapse, and lateral movement.
- 29
Exterior drain openings must be protected from:
Explanation
IPC 304.4: Strainer plates and open pipes must be protected from rodent entry.
- 30
For condensate drains serving air-conditioning equipment, the minimum drain diameter for equipment up to 20 tons is:
Explanation
IPC 314.2.2: The minimum condensate drain pipe size is 3/4 inch for air conditioning units up to 20 tons of refrigeration capacity.