Topic 02 · General Regulations
Set D Questions 31 to 40
- 31
What slope is required for a horizontal condensate drain pipe?
Explanation
IPC 314.2.1: Condensate drains shall be pitched at a slope of not less than 1/8 inch per foot (1-percent slope).
- 32
AC condensate discharge to streets may occur:
Explanation
IPC 314.2.1: Condensate shall not create a nuisance in streets or alleys.
- 33
Where an auxiliary (secondary) drain pan is required for an AC cooling coil in an attic, what is the minimum pan depth?
Explanation
IPC 314.2.3: An auxiliary drain pan must have a minimum depth of 1.5 inches.
- 34
The auxiliary AC drain pan pipe must discharge to:
Explanation
IPC 314.2.3: The secondary drain pan pipe shall discharge to a conspicuous point of disposal to alert occupants of a primary drain blockage.
- 35
What is required in a condensate drain line to prevent sewer gas from entering the HVAC ductwork?
Explanation
IPC 314.2.4: Condensate drains must be trapped (typically with a water seal) in accordance with the equipment manufacturer's instructions.
- 36
Public sewer connections require:
Explanation
IPC 301.3: All sewer connections require local authority approval.
- 37
Plumbing materials must be installed per:
Explanation
IPC 303.8: Materials must be per manufacturer instructions and code.
- 38
Used fixtures may be installed if:
Explanation
IPC 301.2: Used materials require code official approval confirming code compliance.
- 39
Water treatment devices must be:
Explanation
IPC 302.2/608: Water treatment devices need official approval and backflow protection.
- 40
Exterior wall annular spaces must be sealed with:
Explanation
IPC 304.4: Exterior wall penetrations must be sealed to prevent rodent entry.