Topic 07 · Indirect/Special Waste
Set A Questions 1 to 10
- 1
According to IPC Chapter 8, which of the following fixtures MUST discharge through an indirect waste pipe?
Explanation
IPC 802.1.1: Sinks used for the preparation of food or washing of equipment and utensils used in the preparation of food shall discharge indirectly through an air gap.
- 2
What is the minimum required air gap distance for an indirect waste pipe?
Explanation
IPC Table 608.15.1 and 802.3.1: The air gap shall be a minimum of twice the effective opening of the indirect waste pipe, but in no case less than 1 inch.
- 3
An indirect waste pipe discharging into a floor sink (receptor) using an "air break" must have its termination point located where?
Explanation
IPC 802.3.2: An air break shall be provided by terminating the indirect waste pipe below the flood level rim of the receptor and above the trap seal.
- 4
Clear-water waste (e.g., cooling water, condensate) is required to discharge into the drainage system through:
Explanation
IPC 802.1.4: Clear-water waste must be discharged through an indirect waste pipe into an approved receptor.
- 5
Where food or beverages are stored or prepared, floor drains must be:
Explanation
IPC 802.1.1: Floor drains in areas where food is stored/prepared must not be subject to backflow that would contaminate the food space.
- 6
Can you install an indirect waste receptor (like a floor sink) inside a toilet room?
Explanation
IPC 802.4: Waste receptors shall not be installed in any toilet room, bathroom, or unventilated space, to prevent unsanitary contamination of the receptor area.
- 7
An indirect waste pipe that exceeds ____ inches in developed length must be trapped.
Explanation
IPC 802.3: Indirect waste pipes shall be trapped where they exceed 30 inches in developed length from the fixture outlet to the receptor.
- 8
Are you permitted to put a trap on the end of a clear-water condensate drain terminating into an air gap?
Explanation
While plumbing codes do not mandate trapping all condensate lines, HVAC mechanical codes/manufacturers often require a condensate trap to handle unit negative pressure.
- 9
Waste water from a commercial dishwasher must discharge through:
Explanation
IPC 802.1.6: Commercial dishwashers typically discharge through an air gap or air break into a floor sink/receptor.
- 10
Can you install a waste receptor inside a crawl space?
Explanation