Topic 07 · Indirect/Special Waste
Set B Questions 11 to 20
- 11
What is the required minimum height of a clothes washer standpipe above the trap weir?
Explanation
IPC 802.3.3: A standpipe shall extend a minimum of 18 inches and a maximum of 42 inches above the trap weir.
- 12
What is the maximum permitted height of a clothes washer standpipe above the trap weir?
Explanation
IPC 802.3.3: A standpipe shall not exceed 42 inches above the trap weir.
- 13
Can the trap for a clothes washer standpipe be installed beneath the floor?
Explanation
IPC 802.3.3: Standpipe traps shall be installed above the finished floor. (Access to clear the inevitable lint and suds blockages is imperative).
- 14
What is the minimum size of a standpipe serving a clothes washer?
Explanation
IPC 406.2: The standpipe and trap serving an automatic clothes washer shall be a minimum of 2 inches in diameter.
- 15
How high above the surrounding floor must a hub drain extend?
Explanation
IPC 802.4.2: A hub drain shall extend at least 1 inch above a waterproof floor.
- 16
An air gap on a water supply line or indirect waste pipe guarantees protection against which hazard?
Explanation
An air gap provides a physical break between the supply/discharge and the receiving vessel, utterly preventing back-siphonage or backpressure contamination.
- 17
Waste water discharging into the public sewer system normally cannot exceed what temperature limit?
Explanation
IPC 803.1: Waste water exceeding 140°F shall not discharge directly into the drainage system; it must be intercepted and cooled first.
- 18
If a commercial boiler blows down water at 180°F, what piece of equipment must receive the discharge before it enters the sanitary drainage system?
Explanation
IPC 803.1/803.2: High-temperature waste must discharge into an approved cooling interceptor or receptacle to lower the temperature to 140°F or less before entering the drainage system.
- 19
If a chemical laboratory sink handles corrosive acid, what must the drain pipe and trap be made of?
Explanation
IPC 803.2/803.3: Special wastes that are corrosive must be directed via specifically approved acid-resistant pipe to a neutralizing basin/device before discharging into the sanitary sewer.
- 20
What is the purpose of a limestone neutralizing basin or tank in a school chemistry laboratory?
Explanation
Acid-neutralizing tanks feature limestone chips which react specifically with acidic lab wastes to chemically neutralize them before they enter standard cast-iron or PVC drainage piping.