Topic 07 · Indirect/Special Waste
Set D Questions 31 to 40
- 31
A standpipe serving a clothes washer must connect to a trap. If the standpipe is 30 inches tall, is this acceptable?
Explanation
IPC 802.3.3: 30 inches is legally compliant as it is >18" and <42".
- 32
Can a single 2-inch trap and standpipe serve two washing machines simultaneously?
Explanation
A standard 2-inch standpipe/trap is rated for the flow of a single laundry machine. Connecting two can cause overflow/suds backup.
- 33
How is a "deep seal trap" defined when considering specialty waste receptors?
Explanation
Standard traps are 2-4 inches deep. Deep seal traps feature longer dip tubes creating a seal >4 inches to resist evaporation and violent pressure fluctuations.
- 34
Where the discharge of an indirect waste pipe is highly susceptible to producing foam or suds, the receptor must:
Explanation
Receptors handling detergents must be appropriately sized and installed (e.g. suds pressure zones) to avoid suds overflowing onto the floor.
- 35
Can an indirect waste pipe be constructed entirely of garden hose?
Explanation
IPC 802.2: Indirect waste pipes must comply with standard drainage pipe material codes, unless it's a specific manufactured appliance discharge hose.
- 36
Must indirect waste pipes be pitched/sloped?
Explanation
IPC 802.2: All drainage piping, direct or indirect, relies on gravity and must be uniformly sloped (e.g. 1/4 inch per foot) towards the receptor.
- 37
An air break differs from an air gap in that:
Explanation
Air Gaps prevent any physical possibility of back-siphonage. Air Breaks terminate above the trap seal but below the flood level rim, meaning they are less protective than Air Gaps but adequate for some clear water/indirect wastes.
- 38
Which is acceptable for the discharge from a potable water pressure relief valve (T&P valve) on a water heater?
Explanation
IPC 504.6: T&P relief valve discharge must never be directly connected to the sewer; it must discharge indirectly via an air gap to a safe location.
- 39
For an air gap protecting an indirect waste pipe measuring 1.5 inches in diameter, what is the required vertical distance of the gap?
Explanation
The air gap must be twice the effective opening. 1.5 inches * 2 = 3.0 inches.
- 40
May an indirect waste pipe have a cleanout installed in it?
Explanation
IPC 802.2: Indirect waste piping must be installed to permit ready access for flushing and cleaning, heavily implying/requiring cleanouts at offsets.