Topic 07 · Indirect/Special Waste
Set E Questions 41 to 50
- 41
Swimming pool wastewater (such as backwash from a pool filter) must discharge to the sanitary sewer through:
Explanation
IPC 802.1.5: Swimming pool drainage and backwash must discharge through an indirect waste pipe to protect the pool water from sewage backups.
- 42
Which of these is NOT an approved indirect waste receptor?
Explanation
Handwashing lavatories cannot serve as receptors for indirect waste to prevent splashing industrial/food/chemical waste onto users washing their hands.
- 43
If a floor sink (receptor) receives discharge from a commercial ice machine, must the floor sink itself be trapped and vented?
Explanation
Even though it receives indirect waste, the receptor itself is intimately connected to the foul sanitary sewer and must have a trap and vent to stop sewer gas from entering the room.
- 44
A commercial food-prep sink drain must utilize an air ____, not just an air ____.
Explanation
IPC 802.1.1: Food handling requires the absolute protection of an air gap (terminating above the flood rim). An air break (terminating below the flood rim) is insufficient for food prep.
- 45
What happens if you connect a culinary (food) sink directly to the sanitary drainage system without an indirect air gap?
Explanation
Direct connections allow sewer backups to reach the sink bowl. An air gap ensures sewage would spill onto the floor instead of entering the food-prep sink bowl.
- 46
Does the condensate from a residential air conditioning cooling coil require an air gap or air break?
Explanation
IPC 802.1.4: Clear-water waste such as A/C condensate must discharge via an indirect waste pipe utilizing an air break or air gap.
- 47
The minimum size of an indirect waste pipe is generally governed by:
Explanation
Indirect waste pipelines must be sized at least as large as the outlet tailpiece of the fixture or equipment they are draining to prevent bottlenecking.
- 48
When an elevator pit requires a sump pump, where must it discharge?
Explanation
Elevator pit sumps (which may contain oil-sensing pumps or simply clear water) must discharge to an indirect waste receptor or an approved storm system, not directly hard-piped to sanitary.
- 49
Must special or indirect waste piping be labeled or marked in commercial buildings?
Explanation
Special waste piping handling dangerous chemicals usually requires clear identification marking to prevent plumbers from accidentally cutting into a live acid line later.
- 50
What is a "local waste pipe"?
Explanation
Similar to indirect waste, a local waste pipe safely conveys discharge from a specific piece of equipment (like a hospital sink) out to a trapped and vented receptor.