Set A Questions 1 to 10
- 1
According to IPC Chapter 7, what is the minimum required slope for a horizontal drainage pipe that is 2-1/2 inches or smaller in diameter?
Explanation
IPC 704.1: Horizontal drainage piping measuring 2-1/2 inches or less in diameter shall be installed with a minimum fall of 1/4 inch per foot.
- 2
For horizontal drainage piping that is 3 to 6 inches in diameter, what is the minimum required slope?
Explanation
IPC 704.1: Piping from 3 inches to 6 inches requires a minimum uniform fall of 1/8 inch per foot.
- 3
What is the required slope for a horizontal drainage pipe that is 8 inches or larger in diameter?
Explanation
IPC 704.1: For pipe sizes 8 inches or larger, the minimum allowed slope is 1/16 inch per foot.
- 4
Which of the following fittings is NOT permitted for changing direction from a horizontal drain to another horizontal drain?
Explanation
IPC Table 706.3: A sanitary tee is prohibited for changing direction from horizontal to horizontal. It is only permitted for horizontal-to-vertical changes.
- 5
A sanitary tee is approved for use in which of the following changes of direction?
Explanation
IPC Table 706.3: A sanitary tee is permitted only for changes in direction from horizontal to vertical.
- 6
When can a quarter bend (regular 90-degree elbow) be used in drainage piping?
Explanation
IPC Table 706.3: A short quarter bend (short 90) is only permitted for horizontal to vertical flow. Vertical to horizontal or horiz-to-horiz requires a long-sweep or combination of lesser angles.
- 7
What is the Drainage Fixture Unit (DFU) value for a water closet (1.6 gpf flushometer)?
Explanation
IPC Table 709.1: A water closet (both gravity tank and flushometer valve types up to 1.6 gpf) has a drainage fixture unit (DFU) value of 4.
- 8
What is the Drainage Fixture Unit (DFU) value assigned to a residential bathroom group consisting of a water closet, lavatory, and a bathtub or shower?
Explanation
IPC Table 709.1: A bathroom group is valued at 5 DFUs for a 1.6 gpf water closet setup (6 DFUs if the water closet uses more than 1.6 gpf).
- 9
What is the DFU (Drainage Fixture Unit) value for a typical domestic kitchen sink with or without a food waste grinder?
Explanation
IPC Table 709.1: A kitchen sink (domestic), with or without a food waste grinder or dishwasher, has a DFU value of 2.
- 10
A cleanout is required at the base of every ____ within a building.
Explanation
IPC 708.1.4: A cleanout shall be provided at the base of each waste or soil stack.